A

adam.h

For integrated / fixed appliances, having a fused switch spur can you then run t&e to a ko box behind the appliance and connect the flex to t&e via a terminal block? covering with a blanking plate.
 
What does the appliance instructions state. It might state that it has to have a BS1363 plug-top.

Yooj

Most instructions also state " if in doubt consult a qualified electrician"

As a plug top is an accepted method of connection for those less qualified, I don't see a problem with a fused spur unit and a flex outlet plate as an alternative method of connection
 
Most instructions also state " if in doubt consult a qualified electrician"

As a plug top is an accepted method of connection for those less qualified, I don't see a problem with a fused spur unit and a flex outlet plate as an alternative method of connection

Ha, ha, true enough! :)

If for whatever reason the appliance requires servicing at a later date by a 'service engineer', and said service engineer is not a spark, would he, or could he disconnect the flex from the spur?

Yooj
 
Given that a switched fused spur would provide double pole isolation if the fuse removed and it is switched off, the flex outlet plate would be dead and there would be no hazard to the service engineer. The flex outlet is not much different to wiring a plug either can be wired wrong!!
 
Not if the engineer had to remove the appliance, i.e. disconnecting the flex from the spur would require isolation of circuit and removal of the face plate to disconnect the flex, all of which could be achieved by the removal of plug-top from socket.
As you have already stated "... a plug top is an accepted method of connection (and isolation) for those less qualified" and since within the appliances lifetime, it is likely to be maintained far more by those who are not electricians, then I would say it is a poor design if it were not to provide adequate methods of isolation for repair and maintenance.

Yooj
 
disconnecting the flex from the spur would require isolation of circuit and removal of the face plate to disconnect the flex
Yooj


The flex is not connected to the spur!! see the first post!!. Disconnecting the flex from a flex outlet plate would not need the whole circuit isolating as the spur would isolate the supply to the flex outlet plate
 
ring into fused switched spur then down to a flex plate which then connects to the appliance. So means of isolation are ther from the fused switch. Same princible as having a plug but this is wired to a fixed plate. rather then a removable plug.
 
Fused spur or flex outlet plate...the point being that there is a requirement to to disconnect and reconnect cabling into terminals. Something I would think a service engineer would unlikely do.

This is the reason that all appliances which are fed via a plug-top have a moulded plug-top fitted by law to the flex, mitigating the need to cut the plug-top off, strip the flex and connect to a terminal block.

That aside, I stand by the fact that doing it this way is a poor design simply because a plug-top is an accepted method of isolation for lay-persons, there is no need to disconnect cables for maintenance etc, and a flex outlet plate solution is a more expensive one than a socket-based solution since you now need to factor in the flex outlet and an FCU instead of just a socket and DP switch both of which are cheaper than the respective alternatives.

You have to ask yourself what is being achieved with FCU and flex-outlet method in terms of safety and functionality...I would say the nett gain is zero, or less than zero, since you now have the added time to wire in the appliance instead of just plugging it in. Then you have the nett-loss for the cost of ownership, since any subsequent maintenance/repair which requires the appliance to be removed/replaced now needs it to be disconnected rather than just unplugged.

Whilst the FCU/Flex outlet is not an issue, it just unnecessarily adds costs and complicates installation for no quantifiable benefit.

Yooj
 
they are fixed appliances, so if you used just a 13A socket you have no means of isolation until you remove the appliance. If it is wired into a flex outlet which is supplied from a switched fused spur then you can isolate the supply first and then remove the appliance.
 
But you would use a DP appliance switch above the counter top (still cheaper than a FCU) which isolates the socket...remove the appliance, remove the plug. Quicker, cheaper, more practicable.

Yooj
 
This is the reason that all appliances which are fed via a plug-top have a moulded plug-top fitted by law to the flex, mitigating the need to cut the plug-top off, strip the flex and connect to a terminal block.

And I always thought the plug top law came in to cut down on the number of badly connected and wrongly fused plug tops fitted by joe public

That aside, I stand by the fact that doing it this way is a poor design simply because a plug-top is an accepted method of isolation for lay-persons, there is no need to disconnect cables for maintenance etc, and a flex outlet plate solution is a more expensive one than a socket-based solution since you now need to factor in the flex outlet and an FCU instead of just a socket and DP switch both of which are cheaper than the respective alternatives.

Don't agree that your method is cheaper, accessory costs I have looked at the FCU / FO are cheaper than your arrangement. Not all equipment is required to have plug tops fitted by law therefore adding the cost of a plug top and additional connection time increases the costs of your method. While you may feel it is poor design, without the full details of the installation and design reasoning it is difficult to say

You have to ask yourself what is being achieved with FCU and flex-outlet method in terms of safety and functionality...I would say the nett gain is zero, or less than zero, since you now have the added time to wire in the appliance instead of just plugging it in. Then you have the nett-loss for the cost of ownership, since any subsequent maintenance/repair which requires the appliance to be removed/replaced now needs it to be disconnected rather than just unplugged.

Whilst the FCU/Flex outlet is not an issue, it just unnecessarily adds costs and complicates installation for no quantifiable benefit.

Given the number of plugs and sockets in inaccessible places I have replaced due to overheating / burning over the years I think that hard wiring does have it's advantages and is a design plus. Given the reliability of appliances the gains / losses of each method are negligable and could be argued for a long time
 

Reply to appliance flex to t&e in the Australia area at ElectriciansForums.net

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
376
As an aside. I have seen patress/sockets fitted upside down under kitchen units with an appliance plugged in. The sockets were firm and not moving...
Replies
4
Views
234

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top