In fact, in light of a recent thread I do have a question. There seems to be some conflicting information concerning the sequence to derive Ib. From a number of different online sources, actually. It has introduced an element of doubt, so I'd be grateful for confirmation and / or a correction. Keeping it local, from the thread I link to below -
http://www.electriciansforums.net/e...-forum/30644-calculating-lb-voltage-drop.html
Can someone confirm this? I have some other questions on diversity right now, but will hold back for the time being.
http://www.electriciansforums.net/e...-forum/30644-calculating-lb-voltage-drop.html
Now I understand the Ib <= In <= Iz. However, High Tower seems to suggest that you apply both diversity and the various correction factors to derive your design current, Ib. I believe that to be incorrect, as the value for Ib is found after the application of diversity, if needed, then the correction factors are applied to In, the nominal rating of the selected protective device.Apply diversity, apply de-rating factors, such as insulation, ambient temp, 3036 rule etc, that will give you your IB then MV/M/A x IB x L / 1000
Can someone confirm this? I have some other questions on diversity right now, but will hold back for the time being.