applying diversity | Page 2 | on ElectriciansForums

Discuss applying diversity in the Australia area at ElectriciansForums.net

Joined
Jan 21, 2011
Messages
581
Reaction score
34
hi guys

ive got myself a little confused here when trying to calculate a max demand figure for the installation below.

60amp TNCS supply to a bungalow.

1x 30A Ring Main
1x 30A cooker unit(with socket)
1x 40A Shower (8.5kw)
2x 20A Radials
1x 5A Lights (7x100w)

using table 1B app 1 OSG

ring main (30a) no diversity = 30A
cooker unit(30a) 10A+30%(fl)+5A =24A
shower(40a) no diversity = 36.9A
radial(20a) 40% = 8A
radial(20a) 40% = 8A
lights 66% =3.04A

using these figures it comes out at a diversified current of 109.9Amps what am i forgeting as this cant be right can it? do i have to apply diversity to the diversified currents

when i use my usual method of adding up the MCB's and then multiplying by 0.4

40+30+30+20+20+5 x 0.4 = 58 Amps

which is what id expect. any help would be appreciated.
 
hi guys

ive got myself a little confused here when trying to calculate a max demand figure for the installation below.

60amp TNCS supply to a bungalow.

1x 30A Ring Main
1x 30A cooker unit(with socket)
1x 40A Shower (8.5kw)
2x 20A Radials
1x 5A Lights (7x100w)

using table 1B app 1 OSG

ring main (30a) no diversity = 30A
cooker unit(30a) 10A+30%(fl)+5A =24A
shower(40a) no diversity = 36.9A
radial(20a) 40% = 8A
radial(20a) 40% = 8A
lights 66% =3.04A

using these figures it comes out at a diversified current of 109.9Amps what am i forgeting as this cant be right can it? do i have to apply diversity to the diversified currents

when i use my usual method of adding up the MCB's and then multiplying by 0.4

40+30+30+20+20+5 x 0.4 = 58 Amps

which is what id expect.
any help would be appreciated.

In reality, you would be hard pushed to see even that 58Amps flowing in your bungalow!! Even if you did, it would only be for a few minutes at most. ...lol!!
 
I think the max demand calculation needs a rethink. It works fine if its a small house with six circuits, but goes to poo when its a large barn conversion with six socket circuits, six lighting circuits, in a twenty way board!
 
just a thought i have.
32x4 rings
16x1 radial combi boiler
40x1 cooker
6 x4 lights

total 208x0.4=83.2 amps
at the moment it has a 60 amp main fuse and working fine,will get dno to put larger one in though.
the chances of them using half the load would be something though
 
hi guys

ive got myself a little confused here when trying to calculate a max demand figure for the installation below.

60amp TNCS supply to a bungalow.

1x 30A Ring Main
1x 30A cooker unit(with socket)
1x 40A Shower (8.5kw)
2x 20A Radials
1x 5A Lights (7x100w)

using table 1B app 1 OSG

ring main (30a) no diversity = 30A
cooker unit(30a) 10A+30%(fl)+5A =24A
shower(40a) no diversity = 36.9A
radial(20a) 40% = 8A
radial(20a) 40% = 8A
lights 66% =3.04A

using these figures it comes out at a diversified current of 109.9Amps what am i forgeting as this cant be right can it? do i have to apply diversity to the diversified currents

when i use my usual method of adding up the MCB's and then multiplying by 0.4

40+30+30+20+20+5 x 0.4 = 58 Amps

which is what id expect. any help would be appreciated.



I think we missed something in the OP.
When you do by OSG, you not going by the fuse size, you going by the load size, so for cooker you apply all that 30% and everything to the load not fuse, unless it really draws 30A as you say, but that means your cooker is 6.9kW, is that correct.
And shower only draws 37A if to go by load, 8500/230=37A
But anyway, to do by OSG would be a big sum, I like everyone else, go by 40% rule.

Best regards: Al
 
Overcompensation it may be.

But I would rather go with the guidance and instruction of the nationally recognised productions in the court of law than guess work.

Overcompensation, ....that has to be the understatement of the year!!

Come on Widdler, we both know that the criteria within BS 7671 and it's guide doesn't work and come to that has never worked!! I have never seen or known of a single Electrical Design Engineer/Consultant etc, ever use them either!!!

You may need to support and use them as a collage lecturer, ...but they are going to be of little use to anyone outside that collage classroom...
 
- - - Updated - - -

Overcompensation, ....that has to be the understatement of the year!!

Come on Widdler, we both know that the criteria within BS 7671 and it's guide doesn't work and come to that has never worked!! I have never seen or known of a single Electrical Design Engineer/Consultant etc, ever use them either!!!

You may need to support and use them as a collage lecturer, ...but they are going to be of little use to anyone outside that collage classroom...


I'M DONE WITH THIS.
 
the OSG and bs7671 only give very basic guidlines on diversity , mainly for domestic installs with very conservative figures.
move onto big commercials etc , then diversity takes on a much more important and complex role , otherwise we'd be using 25mm for lighting on the top floor of 6 storey office block ;-)

so at this point the designer has to go beyond suggested " one size fits all" tables and look more closely at assessing demand.
 

Reply to applying diversity in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top