Arc Fault Detection going global ... | on ElectriciansForums

Discuss Arc Fault Detection going global ... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Wilko

-
Arms
V.Nearly Esteemed
Joined
Jul 28, 2016
Messages
6,245
Reaction score
7,157
Location
Berkshire
Well I ventured out into the kungflu today and one of the other items picked up was Professional Electrician for December. So I’m having a cuppa and reading, as I do. The article on p33 is about Amendment 2 to the 18th Edition. All good so far. Then I read that they are proposing all socket outlets 32A or less be AFDD. Is it just me, or has the world gone loopy loop?
[ElectriciansForums.net] Arc Fault Detection going global ...
 
I can see ALL sorts of problems in industrial situations of AFDD causing tripping problems.

And no one yet has faced the problem of testing (either the AFDD or the circuit it is tripping on).
 
There were some exceptions to that regulation in the draft, that they missed out on in the article.

421.1.7 Arc fault detection devices (AFDD) conforming to BS EN 62606 shall be provided for single-phase
ACfinal circuits supplying socket-outlets andfixed current-using equipment with a rated current not exceeding 32A.
AFDDs conforming to BS EN 62606 are recommended for all other final circuits.
AFDDs may be omitted where unexpected disconnection of the circuit could cause danger, for example:
(i) the exciter circuit of a rotating machine
(ii) the supply circuit of a lifting magnet
(iii) a circuit supplying a fire extinguishingdevice
(iv) a circuit supplying a safety service, such as a fire alarm or a gas alarm
(v) a circuit supplying medical equipment used for life support in specific medical locations where an IT
system is incorporated
(vi) lighting circuits in dwellings.
Where used, AFDDs shall be placed at the origin of the circuit to be protected.
The use of AFDDs does not obviate the need to apply one or more measures provided in other clauses in this
standard
 
Last edited:
But more to the point - for the claim of improved safety there would need to be evidence. Has this been sighted?
This is the crux of the matter. Yes fires are terrible and to be avoided, but the majority of them appear to be faulty appliances (e.g. tumble dryers catching fire due to clogging with lint) or in many cases due to seriously deficient design & installation.

So where is the cost-benefit analysis of the number of fires that AFDD might stop, versus the wider economic impact of the higher cost and resulting changes in consumer behaviour.

After all the significant cost of AFDD will cause a lot less "optional" CU upgrades and that alone presents a fire risk due to the lack of RCD (which will trip on most parallel arcs), as well as a risk of a fatal shock. It is not simply a case of "make it so and they will just pay up", and there are unscrupulous folk who will quote cheap and do a dangerous job that many won't know about until it is too late.
 
AFDDs are redundant at best in the IEC market. Period. I know because thats exactly what UL and manufacturers were imitating when they created them. By their own admission EU/AS/NZ wiring practices already detect arcing faults.
 
This is the crux of the matter. Yes fires are terrible and to be avoided, but the majority of them appear to be faulty appliances (e.g. tumble dryers catching fire due to clogging with lint) or in many cases due to seriously deficient design & installation.

So where is the cost-benefit analysis of the number of fires that AFDD might stop, versus the wider economic impact of the higher cost and resulting changes in consumer behaviour.

After all the significant cost of AFDD will cause a lot less "optional" CU upgrades and that alone presents a fire risk due to the lack of RCD (which will trip on most parallel arcs), as well as a risk of a fatal shock. It is not simply a case of "make it so and they will just pay up", and there are unscrupulous folk who will quote cheap and do a dangerous job that many won't know about until it is too late.

Serial arcing is the end stage of joule heating, assuming combustion has not already initiated.
 
AFDDs are redundant at best in the IEC market. Period. I know because thats exactly what UL and manufacturers were imitating when they created them. By their own admission EU/AS/NZ wiring practices already detect arcing faults.

Out of interest, which existing EU wiring practices detect arc faults?
 
You folks probably have no idea of what we 'yanks' have gone through with this new 'technology' in the last 20 yrs, but i'll wager you'll not like them very much ~S~
There is definately that feeling of a "solution for a problem" that does, nt exist about these devices. I think it's present in the mind of many sparks. We would all be more than happy to be proved wrong as legitimate improvements should be welcomed. But the "proved wrong" part is the issue. Where is the overwhelming evidence for the need of thus device.?
 
You folks probably have no idea
Ah but we do! I read with great interest your previous exhortations for us to rise up and refuse AFDD. The evidence you presented was most compelling and finally I am swayed to your presentation of the redundancy of AFDD in the UK as our existing installations are adequate for arc detection. However my advice is to buy shares in AFDD! pronto! Well if it gets passed in the regs as compulsory. Thank goodness I am retiring soon. I shall get the popcorn and watch this space with great glee and gloating at my good fortune of not having to get involved in the forthcoming mess.
 

Reply to Arc Fault Detection going global ... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top