Hi All,

Just wanted to see what peoples opinion is

is installing a 30ma Split load board compliant/ non compliant under the 18th Edition or you have to use RCBO's for each final circuit?

BS7671:2018, Page 155 regulation 531.3.5.2 is a note which says on TN systems which states " Exept where particular restrictions on selectivity applies; Several circuits may be protected by the same device"

Views?
 
It all depends on your interpretation of the regs.
IMO, Yes they are compliant.
This was discussed in another thread where some members said that they are not compliant.
I will see if I can find it.
 
Hi All,

Just wanted to see what peoples opinion is

is installing a 30ma Split load board compliant/ non compliant under the 18th Edition or you have to use RCBO's for each final circuit?

BS7671:2018, Page 155 regulation 531.3.5.2 is a note which says on TN systems which states " Exept where particular restrictions on selectivity applies; Several circuits may be protected by the same device"

Views?
Your last paragraph gives you the answer. This is new to the 18th Ed.
 
I believe they are still compliant. However, in the regs, it does state selectivity and also there is another reg that says you shouldn’t exceed 30% of the rcd tripping current, which I believe is around 9ma. So I believe it is preferable to use individual rcbo as it reduces the amount of leakage current on a circuit and makes more of an easy installation. But if you can calculate how much earth leakage is in a group of circuits there is nothing wrong with using a dual rcd unit. That is my opinion anyway.
 
There is also the new reg that states that RCDs must have overcurrent protection if the upstream fuse does not offer this and the total rating of the devices protected by the RCD exceeds the rating of the RCD.
Easier to use RCBOs all round and offers a better installation for the customer and for future work.
 
There is also the new reg that states that RCDs must have overcurrent protection if the upstream fuse does not offer this and the total rating of the devices protected by the RCD exceeds the rating of the RCD.
Easier to use RCBOs all round and offers a better installation for the customer and for future work.
so a RCD protects 4 circuits (as normal in a dual RCD board), 1 32A cooker, 1 32A sockets, 1 6A lights, 1 16A c/h. total rating of MCBs 86A. RCD rating 80A. so not compliant. however those circuits will not draw anywhere near 80A as long as the sun shines. has the world IET gone mad?
 
so a RCD protects 4 circuits (as normal in a dual RCD board), 1 32A cooker, 1 32A sockets, 1 6A lights, 1 16A c/h. total rating of MCBs 86A. RCD rating 80A. so not compliant. however those circuits will not draw anywhere near 80A as long as the sun shines. has the world IET gone mad?
According to new regs that arrangement would be compliant if backed up by a 60A or 80A DNO fuse or <80A OCPD of another type. Diversity is allowed to be applied to this if the RCD manufacturer allows, but none will.

Hager responded to this by changing all their dual RCD boards to 100A RCDs to make it a no brainer.
 
i agree, at present though they're just too expensive for joe public to afford.
Many electricians have been installing RCBO consumer units for many years. I personally have not installed a dual RCD board for a few years now.
There are many affordable options available.
 
Good question.

A really easy safe answer would be to say yes they are still compliant, but RCBO boards are better.

Not so safe answer.

Ifeel split boards are now virtually obsolete and feel with the regulations now encouraging us to take into account disruption in the event of a fault splitting an installation between 2 RCD’s it possibly not so good design especially with the average domestic house having 8 separate circuits these days.
 

Reply to Are 30mA split load consumer units non compliant under 18th edition in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top