Hi All,

Just wanted to see what peoples opinion is

is installing a 30ma Split load board compliant/ non compliant under the 18th Edition or you have to use RCBO's for each final circuit?

BS7671:2018, Page 155 regulation 531.3.5.2 is a note which says on TN systems which states " Exept where particular restrictions on selectivity applies; Several circuits may be protected by the same device"

Views?
 
If you could fit an rcbo board for just a fraction more money than a split rcd board then why on earth would anyone fit the rcd board.
an rcbo board or better in every way thinkable

It's only a fraction more if you use lewden or the like.

How often are you expecting the RCD to trip in a normal domestic?
 
very rarely, but when it happens the disruption to loosing half the houses electrics is why RCD split board is a poor choice.

Granted it's not the best solution but it is a cost effective one and compliant.

I certainly would not call it a poor choice as like everything there is a cost vs benefit element to it.
 
They are still compliant, and the disruption to end user is minimised if half the house goes off is initial design.
Upstairs lights with downstairs socket....
Cooker on different rcd to kitchen sockets

It would be simpler for us just to say it has to be all rcbo now to comply, but mr customer can find split boards in his local diy.com retailer
 
Commonly installed but the regs do state that the failure of one circuit shouldn't effect another circuit.

Similar situation with SY cable. It's not a BS7671 recognised cable but widely used.
More to do with one circuit breaker protecting one circuit disconnecting will not effect another , as the regulations allow more than one circuit to be collectively protected by one rcd.
 

Reply to Are 30mA split load consumer units non compliant under 18th edition in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
701
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top