i had my niceic inspection one of the jobs was some flats that had been referbed same thing with the gas and water. but he insisted i run the earths to the incoming position just in case of any later alterations. so i would say run the earths in but dont conect them.
 
What you want is a low earth path creating a very high fault current and so ensuring the overcurrent protective device will blow in time. The ESC and other agree on 0.05 as this will cover a 0.4 disconnection time on a 100a HRC will will be about the largest you will get in a domestic property.

Sorry Scotsparky, but that isn`t the reason that 0.05 ohms is stated as the max permissible resistance between extraneous & exposed conductive parts - which is what is being discussed here. The correct reason was actually given by Markthesparky.
What you`re referring to is applicable where the required disconnection times cannot be achieved by breakers/RCD`s so supplementary bonding is utilised to ensure disconnection within the prescribed times.

Altho the need to ensure adequate conductance is common to both, in the context of Main Protective Bonding to water & gas services, it`s done to ensure no dangerous differences in potential exist between the various conductive parts - achieving equipotentiality. :)

T
 
Hi all.
Why does water and gas cause a major headache for electricians. Do we deserve this agro ???? The point of all this bonding conductor stuff ( as we already know ) is to cover ourselves from pipework that is exposed to human touch, getting a potential that could be harmful with reference to earth.

Tell me why plumbers aren't made responsible for ensuring their own installation is correctly earthed ?

Do what you can. As long as you can walk away from the site and be confident you've done what you are expected to do, then that's it.

I was told that if incoming pipework was not metallic ( so no conductive path back to earth ), then main bonding wasn't necessary.

But, like you say, what about radiators with a minimal amount of copper pipe work attached ? Well, just like previous wiring regs, which insisted that metallic windows and doors required bonding, things went just too far !!!!!

I would say that radiators fed from plastic pipework don't need bonding. As long as the situation is in writing describing this, then you are ok.
 
Hi all.
Why does water and gas cause a major headache for electricians. Do we deserve this agro ????

Friday, prior to starting job, checked bonding 10mm & in place...
Gas - no prob.
Water - at what appears to be main stopcock, no bonds in sight...

Upon enquiring, kitchen was fairly recently refurbed. Made a nice neat job of hiding the bond(s) completely behind sink units. Say bond(s) due to how they`d very thoughtfully bonded hot as well as cold (conscientious or what :rolleyes:) but unfortunately placed them in totally inaccessible position, >600mm from incomer & after 2 branches. Classy...

Measured 0.03 ohms.

Thankfully, the peeps at Elecsa are reasonable folk & take these things in their stride... mark down as deviation & carry on :)


But, like you say, what about radiators with a minimal amount of copper pipe work attached ?

I would say that radiators fed from plastic pipework don't need bonding

Usually not. Whenever in doubt, do IR test between known earth & extraneous part - anything above 20-25k, don`t bond.
 
Evening all,

firstly a huge thanks to everyone for the comments and suggestions - I think this is where this forum and its contributors are at their best.

Secondly, apologies if I've appeared a bit 'mute' on this thread - unfortunately I've been working late this evening and only just got to the PC.

Based on the info I've been given and references from NIC, Paul Cooke etc, I'm sure I don't need to run in main bonds, but after today's experience of the plumber ( same bloke, different job) I'm underwhelmed to put it mildly. Consequently as wisely advised in the thread, I'll run them in anyway just to be on the safe side, even if only for future possible need. Might be overkill, but I'll sleep easier.

Thanks again lads.
 
Of course, problems may well arise in those special locations ( bathrooms ), where you have to ensire that any exposed conductive parts ( take your pick from piepwork and radiators ) are bonded. So you might have to do some supplementary bonding in those loactions.
 

Reply to are main bonds required ??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
597
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
774
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

If you can see a piece of plastic entering from the ground then (as cliff said), it does not need main bonding. I think (not sure) this is reg...
Replies
3
Views
411
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top