M
matthunt
Are any of you seeing High voltage problems in houses with Solar/PV installed in same street?
I attended a call out a few weeks ago due to the fuse board apparently smoking. When i arrived it transpired it was the shower circuit, the voltage measured was 246v and the current 36 amps meaning a 7.5kw shower drawing 8.8kw through a cartridge type Wylex db. The fuse was rated at 30amps and you just could not touch it due to the heat. We all know of the inherant problems with this type of fuse whilst continuing to operate on steady over current. Has anyone else seen this type of problem? as i am aware that multiple PV installs in a street on the same phase will obviously boost the voltage due to the nature of the invertors.
I attended a call out a few weeks ago due to the fuse board apparently smoking. When i arrived it transpired it was the shower circuit, the voltage measured was 246v and the current 36 amps meaning a 7.5kw shower drawing 8.8kw through a cartridge type Wylex db. The fuse was rated at 30amps and you just could not touch it due to the heat. We all know of the inherant problems with this type of fuse whilst continuing to operate on steady over current. Has anyone else seen this type of problem? as i am aware that multiple PV installs in a street on the same phase will obviously boost the voltage due to the nature of the invertors.