I am not an electrician. Can anyone help please?
I have an outbuilding which I am converting into two offices.
The building is currently served by a 16mm armoured cable running underground from my house, the distance is about 100 metres.
Potentially the building could have a maximum of the following appliances:-
2x2kw electric oil filled radiators
1x1.5kw electric oil filled radiator
Hand wash 2.5kw
Electric Kettle 2.5kw
Saniflo 400 watts
Vacuum Cleaner 1kw
4 Fluorescent Lights
2 Computers
Total aprox 13kw
Will the existing 16mm cable be adequate or will I have to have it replaced with a 25mm armoured cable.
Thank you
If you are using the office for yourself and are concious on what you are using together then the 16mm on a 25A MCB should be ok. Must be a big shed for that many heaters?
I would go with the upgrade however and get a fully detailed quote before placing the order.
I would be using a fuse at source otherwise it could be a long walk when something trips out.
You're obviously in possession of warm clothing.
I get 23.91 Amperes with just the heaters on full balls.
i could not be arsed to work out the VD as books are in van. however, for wtat it would cost to replace the 16mm cable versus exceeding the 3% for lighting, I'd fit LED lights which are happy with a slightly reduced voltage and sod it. at the end if the day, it's only a shed, not a hospital operating theatre. tin hat ready.
one help please?
Hand wash 2.5kw
Saniflo 400 watts
Vacuum Cleaner 1kw
2 Computers
Total aprox 13kw
Thank you
Essex
Armoured cable 16mm or 25mm
Cliff C,
Pete999,