Hmmm, Could anybody tell me which table I use for calculating armoured cable sizes in the on-site guide?
I'm self teaching and failing :-(
I'm self teaching and failing :-(
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Armoured Cable Calculations in the UK Electrical Forum area at ElectriciansForums.net
It is not the same, but it is similar.
Same CSA so heat generated for a given current (per unit length) is the same. Same 70C insulation limit on how hot it is allowed to get.
But different outer diameter (so thermal resistance to ambient slight different) for general mounting cases, and typically the use-cases (i.e. "method") are different. E.g. you are unlikely to have SWA run through loft insulation, and similarly you should not be burying T&E directly in the ground.
It’s a great book, really really helpful and informative but, not sure I’ve got to that bit yet. I’ll be reading this a few times over I think.that's a good book, one thing I've not calculated yet is the armour as CPC there's some equation for this isn't there?
The armour as CPC for SWA is not obvious. It usually has larger CSA than the conductors but as it is steel the resistance is around 8 times higher per mm^2. For smaller cables it is often adequate, better in fact than T&E for R2, but for large cables it can fail the adiabatic requirements so you may end up using 3-core for single phase, 5-core (expensive) for three-phase, or running a supplementary CPC of 0.5-1.0 phase size alongside.that's a good book, one thing I've not calculated yet is the armour as CPC there's some equation for this isn't there?
The armour as CPC for SWA is not obvious. It usually has larger CSA than the conductors but as it is steel the resistance is around 8 times higher per mm^2. For smaller cables it is often adequate, better in fact than T&E for R2, but for large cables it can fail the adiabatic requirements so you may end up using 3-core for single phase, 5-core (expensive) for three-phase, or running a supplementary CPC of 0.5-1.0 phase size alongside.
The last page of this data sheet has the info you might be looking for:
Is this mentioned in the books anywhere? just trying to work out if I'm missing it.SWA armour is generally accepted as sufficient cpc for cables up to 95mm. however, on smaller cables it may not be adequate as a bonding conductor.
SWA armour is generally accepted as sufficient cpc for cables up to 95mm. however, on smaller cables it may not be adequate as a bonding conductor.