shaun gold

I recently came across an armoured cable on an ECR that was installed in earthed metal trunking from one dis board to another.
Both ends of the armoured had not been glanded off and the SWA had been taped over. As it is enclosed in the tunking and both ends are in the
distribution boards would this be satisfactory as there is an extra core being used as the CPC so the SWA is not needed.
 
I recently came across an armoured cable on an ECR that was installed in earthed metal trunking from one dis board to another.
Both ends of the armoured had not been glanded off and the SWA had been taped over. As it is enclosed in the tunking and both ends are in the
distribution boards would this be satisfactory as there is an extra core being used as the CPC so the SWA is not needed.

In a word ...NO!!

If your going to use a cable that has been designed to be glanded at each end, then that's what the cable demands. You always use the correct cable type for the installation as presented to you. In his case the wiring should have been conducted in singles of the correct size...

There is also absolutely no requirement for an additional CPC either!! This smacks of a lazy electrician that had a bit of suitably sized SWA on the van, so in it went rather than supplying the correct singles....
 
In a word ...NO!!

If your going to use a cable that has been designed to be glanded at each end, then that's what the cable demands. You always use the correct cable type for the installation as presented to you. In his case the wiring should have been conducted in singles of the correct size...

There is also absolutely no requirement for an additional CPC either!! This smacks of a lazy electrician that had a bit of suitably sized SWA on the van, so in it went rather than supplying the correct singles....

The fact that the cable is SWA in this instance is incidental. OK, its not the cable of choice, I agree, but here I feel that it can be treated as not SWA as the steel conduit provides the protection normally achieved by the armouring.

Stoop nit picking!

EICR? so what code would you give it then?

Me, I wouldn't code it, That's my stance and I'm sticking to it unless someone can convince me otherwise, and I mean with SOUND REASONING, not like the reasoning behind not having neutrals at switches, LOL!
 
mmm hard one. Think somone has been too lazy to strip the armour.

Suppose you could stick a earth clamp around armour sheath and bond it to the trunking to make the sheath earthed.

Not sure if I would code it or not.
 
mmm hard one. Think somone has been too lazy to strip the armour.

Suppose you could stick a earth clamp around armour sheath and bond it to the trunking to make the sheath earthed.

Not sure if I would code it or not.

You could, but with earthed trunking, and a core used as earth, why would you bother? it's no different to a submain run in singles, except all the 'single' cores are in a sheath together. Not the cable I'd use, but not unsafe in any way. Unconventional - yes.
 
mmm hard one. Think somone has been too lazy to strip the armour.

Suppose you could stick a earth clamp around armour sheath and bond it to the trunking to make the sheath earthed.

Not sure if I would code it or not.

I really hope you are not suggesting to put a BS951 clamp around a SWA
 
mmm hard one. Think somone has been too lazy to strip the armour.

Suppose you could stick a earth clamp around armour sheath and bond it to the trunking to make the sheath earthed.

Not sure if I would code it or not.

I really hope you are not suggesting to put a BS951 clamp around a SWA

I have seen a jubilee clip used for the steel wire on a three phase and neutral supply for a lift supply on a construction site. The sparky thought nothing off it. He Was actually quite proud he had managed to squeeze it all into a 32amp 5pin socket . Any one else would be embarrassed to admit it
 
Id like to see the cable calcs of an armoured enclosed in a trunking ;) .... and my input ..... not good practice and very lazy to the extreme it wouldn't have taken long to run a stanley down and rid it of armour, but it should be noted but i wouldn't make too big a fuss as its not really at risk from damage where the armour would be required to be earthed....i think this one off situe would merit a Jobsworth award but its functional as long as the trunking is complete, bet it fails in its use elsewhere like trunking grouping or spacing factors ;)
 
I must say, i am struggling to see a problem with this.

Yes, maybe the SWA should be earthed and glanded off correctly, but as pointed out, it is in trunking so could be "assumed" to be T&E.

Certainly not worth a code, and dare i say, certainly far from unsafe.

All IMO.
 

Reply to Armoured Cable Termination. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
400
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
986
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
2K
Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
289

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top