Armoured cable to garden shed | on ElectriciansForums

Discuss Armoured cable to garden shed in the UK Electrical Forum area at ElectriciansForums.net

banny07

-
Arms
Joined
Aug 2, 2009
Messages
193
Reaction score
39
Hi Guys. Customer want to install some double sockets and few lights in new built garden shed which is 35 meters away from Consumer unit. I suggested 10mm 0r 16mm swa cable as customer want use it as a gym and also install washing machine and tumble dryer in the future. Only route available is through bathroom floor (behind the toilet and under shower tray), then under kitchen unit and through garden(burried) to the shed. Please advise me on this. Thanks in advance
 
If there is a washing machine, then I presume water as well, this may therefore need bonding, which may then need the cable to be 10mm^2 depending upon the earthing arrangements.

The minimum size for bonding may be the controlling size rather than voltage drop, or Zs, or current capacity etc.
 
If there is a washing machine, then I presume water as well, this may therefore need bonding, which may then need the cable to be 10mm^2 depending upon the earthing arrangements.

The minimum size for bonding may be the controlling size rather than voltage drop, or Zs, or current capacity etc.
As cable will pass through bathroom ( on the tiled floor and under the sower tray) do I need to install rcd on the circuit?
 
As cable will pass through bathroom ( on the tiled floor and under the sower tray) do I need to install rcd on the circuit?
Not if it’s getting boxed in.

Yes if you’re planning a joint box in the bathroom to convert cable from T&E to SWA for example.
 
As cable will pass through bathroom ( on the tiled floor and under the sower tray) do I need to install rcd on the circuit?
You would also need some kind of RCD protection if the earthing arrangement at the house is TT. The SWA will have mechanical protection but no fault protection. I would usually fit an S type 100mA. If it's PME of TNS then you wouldn't need the RCD because of ADS.
 
As cable will pass through bathroom ( on the tiled floor and under the sower tray) do I need to install rcd on the circuit?
If it is SWA then usually[1] no as it has the earthed armour so no risk of damage causing the damaging object (screw via headrail, etc) to become live.

[1] The "usually" aspect has been mentioned by @HappyHippyDad in that the above assumes that any fault that shorts out L-Armour will disconnect the power. On a TN supply system that is usually[2] the case, on a TT supply it is virtually impossible so an up-front 100mA/300mA delay RCD is the usual approach.

[2] Even on a TN system you might find a high current sub-main has an end of cable Zs that is too high to meet the 5s disconnection time on the design OCPD. If it is marginal the using 3C SWA[3] so one core is CPC and is connected at both ends of the armour is enough, but if that is not enough, or if the cable cost going that way is ridiculously high, then you might again consider an up-front RCD.

[3] As @Julie. has pointed out, if there are extraneous parts to be bonded and it is TN-C-S then your minimum bond size is 10mm copper (or equivalent). For the steel in SWA that is about 80mm which you only get to on 2C when you have 70mm conductors! Once again you might just consider TT'ing the supply at the building but then you have the issue of earth rods and the risk of driving in to the ground without hitting buried services, etc, so going 10mm 3C (or making very sure all the water pipes are plastic) is usually the simplest route and meets most folk's power demands.
 
Not if it’s getting boxed in.

Yes if you’re planning a joint box in the bathroom to convert cable from T&E to SWA for example.
Why would converting from T&E to SWA require RCD protection? I take it as an almost given that this cable isn't going to be sunk into the wall at any point.
 
Why would converting from T&E to SWA require RCD protection? I take it as an almost given that this cable isn't going to be sunk into the wall at any point.
Rcd to cover anything within a bathroom.
Not serving anything in a bathroom, but a joint would introduce a possibility of a loose connection. Was just an example.
Boxing it in takes it outside the bathroom area if it’s inaccessible..
 
Rcd to cover anything within a bathroom.
Not serving anything in a bathroom, but a joint would introduce a possibility of a loose connection. Was just an example.
Boxing it in takes it outside the bathroom area if it’s inaccessible..
Even an SWA running through a bathroom would need RCD protection (oh what an eyesore that would be!). Don't see why a junction box requires RCD protection for a possible loose connection, it's not there to cover off poor workmanship.
 

Reply to Armoured cable to garden shed in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
684

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top