Having read the draft PV guide edtion 3 out for review, I see very little instances where you would earth or bond an array frame.

I appreciate there are instances where you should but these seem quite rare reading the new guidline, even with transformerless inverters.

is anyone still earthing their array frames when using transformerless inverters or already starting to move over to the new guidelines and keeping the majority of their frames floating??
 
The new guidelines are still in draft form and subject to change. You shouldn't be working to it, no matter how convenient it might be. If you are fitting a transformerless inverter, bond the array frame every time.
 
Thanks Julian,

Thats still my thought process at the moment. I am still earthing / bonding my array frame as per the original guidlelines. Thanks for the response.
 
Thanks Julian,

Thats still my thought process at the moment. I am still earthing / bonding my array frame as per the original guidlelines. Thanks for the response.
I would'nt bond the array unless you can touch the panels from a velux window etc. because your potentially introducing a fault path this was confirmed by ECA
 
my concern with this has always been if there is a fault on the DC cabling causing the array frame to become live without bonding the first you'll know about it is when you fry yourself going up there to investigate. It does concern me having a large metal structure, potentially having potential, so to speak, and no earthing, even with a transformerless inverter. It's a concept I'm having trouble getting my head round.
Without bonding what would stop you getting fried?
Any explanations at a suitably simpleton level gratefully received, I am after all a bear of very little brain!!!
 
Last edited by a moderator:
My last Niceic inspection and Mcs inspection the assessors knew very little about Pv and most of the assessment seemed to be talking about the pv side of the install i was using.
I know that in Germany its common practice to earth all arrays TL or not and if you read the inverter manuals the manufacturer usually reccommends you do so ,even though the Regs/DTI guidelines etc say otherwise
 
We're still bonding frames.

In general, a fault from the panels to the frame shouldn't be that dangerous in itself as there shouldn't be any potential to earth anyway. That is unless I'm missing something.
 
i spoke to window cleaner yesterday who cleans them for 3 of his clients! i said did he shut it down first? no? i did point out if he had ladder on wet grass(silly but true) then he holds on at top to ladder! other hand sponge!!(yes i no they dont use sponges) but u get the idea!!! if fault (voltage) on array he will be a FLYING oops FRYING window cleaner!! but what do i no? nothing thats y i steeeeeer clear of TL invertas unless totaly stuffed!!
 
Big solar
as I understand it, and as I say I do have a conceptual problem with this, if there is a short between the DC and the frame, that frame will hold a potential. it will continue to hold that potential until it is given a path to earth, through a bonding cable if present, or the window cleaner if it isn't!!
 
All elasatictrickery wants to do is get back to it's point of origin.

If a DC pos is touching the array frame, it will do nothing untill it finds the DC neg of the source. It can't flow until that path is made.

This is why bonding DC down to ground is frowned upon, in doing that, you are creating a path.
 
All elasatictrickery wants to do is get back to it's point of origin.

If a DC pos is touching the array frame, it will do nothing untill it finds the DC neg of the source. It can't flow until that path is made.

This is why bonding DC down to ground is frowned upon, in doing that, you are creating a path.

That is my understanding too. The DC +ve is only interested in getting to DC-ve. This means even if the +ve is shorting to the frame, you shouldn't (in theory) get a shock as there is no potential to earth. Kinda like if you were to wire up 10 12V batteries (120v) in series an touch the live terminal. Am I on the right track?
 

Reply to Array frame earthing in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K
Good one . Thanks. I was finding Fluke etc ÂŁÂŁÂŁ!
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top