Interesting thread....
"Also most Tl's will normally have residual currents upto 50mA and with some over ,this is why you should'nt use 30mA Rcd's" - important observation. As is Edexlab's comments about PV arrays having a potential difference present when using TL inverters.
PV arrays will generate parasitic capacitive leakage currents (AC) naturally, especially when there is dew/moisture present in the mornings and things start to warm up. Combine this leakage current with anything inherently produced by the TL inverter and you can often "nuisance" trip a 30mA RCD. This is why SMA, Fronius, PowerOne etc recommend the use of a minimum 100mA trip limit RCD (300mA for PowerOne I think) when fitting their TL inverters. Whether this requirement conflicts with a pre-determined need to fit a 30mA RCD in compliance with wiring regs/BS standards (indirect contact fault protection, for example) is a debatable point.
Interestingly enough, I did hear that bonding your array to earth can exascerbate the generation of capacitive leakage currents by the array.
Btw, these slowly rising capacitive leakage currents can often not be detected by an internal RCMU (residual current monitoring unit) in the inverter as RCMU's typically only identify sudden rises in leakage current and will often not result in disconnection until max 300mA is reached. Relying on the inverter's built-in RCMU to act as a circuit protective (safety) device should not be recommended.
In addition to these naturally generated capacitive leakage currents, if a component of that leakage current is pure DC, with any greater than 6mA amplitude, a Type-A RCD manufacturer cannot guarantee that the RCD will continue to operate within it's required trip characteristics (required as a safety device to conform to its own standard/Reg 133.1.3). Some Type-A RCDs have been seen to have operated up to 30% over their intended trip limit when such DC leakage current components exceed 6mA pure DC. Type-AC RCDs will simply find themselves with a saturated trip coil and will NEVER trip, under fault conditions.
Anyway, I digress somewhat....my take on it is somewhat like this: If you have a TT supply, don't use a TL inverter - or if you can't mitigate against the BS7671 requirement for a 30mA RCD, don't use a TL inverter unless you can ensure that a 30mA Type-B RCD will function without nuisance tripping. If you can use a TL inverter, earth the array and fit a Type-B RCD for AC and DC circuit leakage fault protection. If you're concerned about the risk of lightning strikes then follow the risk assessment (as part of the recent BS7671
443 ammendment) and fit Type2 SPDs to the DC and AC circuits. If an LPS (lightning protection system) is already in place (or you have a TT supply) then fit Type1/Type2 SPDs accordingly depending on whether adequate separation distances are respected from the LPS and the array frame.
See
here and
here and
here for some info that you may (or may not) find useful,
Andy
(don't shoot me if I've completely hijacked the thread, my apologies, it's been a long day and I'm a wee bit tired so apologies if the above makes no sense at all!)