I dont know if this is in the write place but forgive me if its not....

Ive got 2 questions im stuck on if anyone could help please.

1. An insulation resistance measurement taken at theorigin ofthe installation records a value of 1.95mohms. Explain your subsequent actions regarding this vaule of IR

2. In order to comply with BS7671 the instrument used to measure IR must me capable of delivering a current of 1mA. Explain the reason for the requirement.


Thanks
 
A IR result of 1.95MΩ could mean that a latent defect exists. Therefore each circuit should be tested separatly as this will help to indentify whether one particular circuit in the installation has a lower IR value, which possbly indicates a latent defect that should be rectified or whether the low resistance represents the summation of individual circuit IR and as such may not be a cause for concern.
 
All i can see is the output values and the acceptable vaules of an IR tester but nothing to say why these values are so other than leakage current durring normal conditions but thats referring to extraneous condictive parts
 

Reply to the thread, titled "Assignment help!" which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top