I have a compressor to be hard wired into a zone 1 container. The container has a 3 phase + E supply but the compressor requires a 3 phase, N & E. This is not something I have experienced before within an ATEX installation and when researching there is a few discussions on TN-S, IT and TT grounding where neutral and earth are bonded together. Can anyone pass on any advise when it comes to this situation?
 
You cannot just combine the Neutral and Earth from the compressor and connect to the container earth, this will send the return current from any single phase load down the earth wire.
It's somewhat unusual for a compressor to need a neutral, what kind is it and what is the neutral used for? If it's just to run a 240-24V transformer for control voltage, then you could likely modify the compressor to use a 400V transformer. Keep in mind though, any modification to equipment in a ATEX zone will likely have additional regulations.
 

Reply to ATEX Neutral connection in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
673
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
777