Good evening folks
A great forum full of information. I'm not much of a contributor but love dipping in now and again to search for answers to problems I may have.


Currently I am installing a Viessmann Vitoligno 300p biomass boiler.
Quite straight forward really....lots of plug and play.
The problem I am having is with a feed to an auger.
It's situated abut 15 metres away from the boiler.
At the plug for it at the boiler I get a reading of 230 v.
At 15 m point I can get a reading of 180v.MOTOR NOT CONNECTED.
When I connect to the motor (90w) the voltage then drops to 0v.
When I connect a dedicated 230v supply (by passing boiler) the auger runs.
Have tried changing cable ----no difference .
Have tried different sizes of cable ....slight/no difference.
Have checked polarity s, continuity, ir , broken neutrals ,earths.....nothing.
The veissmann tech guy has been out and can't find the prob.
He even changed part of the control panel.
I'm pretty stumped really.
A few people have mentioned that it seems like an internal relay or something which is not making a good contact.


Any way I really appreciate anyone having a look at this post


All the best


P
 
Seem to be fine...have changed a plug as well. Though after digging the bones out of it today that was one of our possible conclusions as well. Sorry I have got no drawings tonight.....may be able to get a wiring diagram of board at a later date!!!
 
Tried this with a lead light...it lit up but was faint!!,
using a fluke mains volage tester and a metrel multi

This is clearly a high impedance (but not open circuit) fault in the supply. The best you can do is to test the supply back from the connector towards the origin with a low resistance indicator (like your lead light or a proper test lamp) until you find the fault. There are some kinds of fault where the older technology testers will be better. The voltage tester and the multi aren't going to be of much use here.
 
So what could be causing the high resistance.....I have tested back to the supply of this connector and have got 230.... But the plugs look fine.....it may still be them I suppose .
 
So what could be causing the high resistance.....I have tested back to the supply of this connector and have got 230.... But the plugs look fine.....it may still be them I suppose .

Yes, but was it still 230 with a load on? With this sort of fault, you need to load the circuit (maybe only a little) and then measure voltages.
 
Is this a brand new boiler and is the installation complete, apart from the hopper auger not working?

If so it seems it must be on a VSD (inverter drive) and the drive is shutting off when it detects the motor connected.

If you've had 230 on the cable to the motor, connected at the boiler end then the problem is in the boiler control.

Definitely a job for Veissmann.
 
Motor is not run through an inverter as far as I can see.
its a brand new boiler and the install is complete all working apart from auger.
could the inverter be an internal component that I can not get to?
no overload settings to alter I'm afraid.
certainly looks like a job for the veissmann tech guy whose back tomorrow morning.
 
photo

heres one
 

Attachments

  • [ElectriciansForums.net] Auger motor - apply load 0 volts?????
    2013-02-28 09.37.39.jpg
    160.2 KB · Views: 41
[ElectriciansForums.net] Auger motor - apply load 0 volts?????
Hi,
Thank you for motor label picture


So,
Second picture:
German induction motor:90w/230v,50Hz, mechanical reduction and & thermal protection.
The only protection you got can cut the power. You got probably 2, 3 wires available.

Only if you are an electrician you could follow the next steps.

a. Identify the phase and neutral properly and see the coil resistance.
(Roughly 500-600 should be all right). If phase- neutral it is ..MΩ the thermal protection from coil needs to be replaced.
b. Energize external the engine (230v).
c. If you keep the mechanical reduction the speed should be 1/min. - very slow.
Thank you. Good luck.

I look forward hearing from you.

Bertt.
 

Reply to Auger motor - apply load 0 volts????? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I believe that if some how can go up on your wire size from the transformer to your place it would make a huge difference in your voltage...
Replies
9
Views
2K
  • Question
No, but I did spend 40 minutes on the phone to the insurance scam she pays into on her behalf, and drive her frozen food to a friends house for...
    • Like
    • Winner
    • Informative
2 3
Replies
66
Views
10K
  • Question
left the system tagged out (isolated) no one is living in it at the mo.thanks for all the feedback. custommer wanted RCBO protection for smoke...
Replies
16
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks