Hi Guys!
I've worked with a few qualified-electricians recently and I'm shocked with the large-scale misconceptions regarding the proper safe-isolation procedure, particularly concerning the function of an AVI (Approved Voltage Indicator).
During the last few weeks I've met several domestic qualified-electricians who have told me not to test between line-earth & neutral-earth because this will trip the RCD/RCBO; they have all advised me to only test between line-neutral. When I confronted them with actual facts and figures, they all refused to acknowledge my comments, arguing otherwise without any form of proof, which I found bizarre?
I'd like to confirm that their advice is incorrect, and I can prove it factually. I use a Kewtech KT1790 Approved Voltage Indicator which seems fairly common amongst electricians, and I'll base my comments on this:
I'm interested to find out if anyone else has encountered this problem? If so, to share this information.
I've worked with a few qualified-electricians recently and I'm shocked with the large-scale misconceptions regarding the proper safe-isolation procedure, particularly concerning the function of an AVI (Approved Voltage Indicator).
During the last few weeks I've met several domestic qualified-electricians who have told me not to test between line-earth & neutral-earth because this will trip the RCD/RCBO; they have all advised me to only test between line-neutral. When I confronted them with actual facts and figures, they all refused to acknowledge my comments, arguing otherwise without any form of proof, which I found bizarre?
I'd like to confirm that their advice is incorrect, and I can prove it factually. I use a Kewtech KT1790 Approved Voltage Indicator which seems fairly common amongst electricians, and I'll base my comments on this:
- The Kewtech KT1790 data-sheet states "This instrument can make measurements between L-PE without tripping RCDs".
- The Kewtech KT1790 data-sheet states that the devices internal-resistance is 200,000 Ohms. Based on this value, we can calculate the current-flow using basic Ohm's Law:
- 230V - 1.15 mA (Standard RMS voltage used for design calculation)
- 245V - 1.22 mA (Highest likely RMS voltage measured)
- 500V - 2.50 mA (Exceeding AC Peak Voltage)
- A common RCD used in domestic properties for additional-protection has an operating-current of 30mA (much greater than the current produced while testing).
- Rarely in specialised circumstances a 10mA RCD is used for certain applications (much greater than the current produced while testing).
I'm interested to find out if anyone else has encountered this problem? If so, to share this information.