B or C type breakers? | on ElectriciansForums
Discuss B or C type breakers? in the UK Electrical Forum area at ElectriciansForums.net
sjm
Hi guys having a brain fade moment.
Any reason why I can't use C type RCBO's instaed of B?
Doing a CU change at a Nursing home and been quoted for C type, currently they're B type.
Board is 3 phase but all breakers are single phase.
Thanks in advance.
Steve.
as long as the Zs is low enough to meet disconnection times. the max. Zs for C type is 1/2 that for a B type of the same rating.
No, they are more susceptible to tripping under inrush/ start up current, nothing to do with sensitivity, in most domestic cases B type should be used. And anywhere that c type is used great attention should be placed on measured ZS value. Unless as has been said, you are employing a RCD, then it matters less
B type = domestic / standard circuits
C type = light commercial, inductive loads, inductive lighting such as loads of flouresents/ mods, etc
D type= heavy commercial/ industrial such as bigger motors/ commercial welding equipment
MCCB = are used in initial distribution and really big loads !!
Anything bigger and your into the realm of HV and ACB's etc and that's the speciality of maniacs like Tony!!
Reply to B or C type breakers? in the UK Electrical Forum area at ElectriciansForums.net
Received guidance from a logical soul on the Kawie Riders forum: Acc Fuse Block Power to BAT LOAD, install new cable from BAT LINE to AUX + (and)...
How did it go?