Hot Neu. / Reverse when on inverter power | on ElectriciansForums
Discuss Hot Neu. / Reverse when on inverter power in the DIY Electrical Advice area at ElectriciansForums.net
Missouri, USA
I have a small camper. When connected to shore power my receptacle tester shows "Correct" (two orange lights). However, when running on my solar generator's (a Jackery Explorer 1000 v2) inverter it shows as "Hot Neu. / Reverse". Is this expected or is there something amiss? If something is amiss then what needs to be done to correct it? (Note: AC appliances seem to be operating without issue when on inverter power.)
Thanks,
Andrew[ElectriciansForums.net] Hot Neu. / Reverse when on inverter power
It may be that when not connected to shore power, there is no ground connection and therefore the tester has no zero volts reference to measure the voltages on either hot or N.
often small inverters like that are designed to run independently to Earth,
an earthing arrangement known as I.T (Isolated "from" Terra)
careful consideration of the manufacturers instructions is required to ensure this is a safe arrangement as sometimes a N-E link should be applied, sometimes a ground rod is required, sometimes the device is only suitable for running a single device and should not be used to power a distribution circuit at all.
...sometimes a ground rod is required...
The camper was designed to run on an inverter, so the equipment should be okay. But for safety, grounding wouldn't be a bad idea. In most of the places I camp, driving a copper rod into the ground 6" wouldon't be a problem. Deeper might be. Is the solution as easy as splicing a 12 ga. wire into the ground wire and running it out to a copper bar?
The solution is to read the instructions and follow the guidance.
Sorry if this sounds like a get out.
What instructions?
  • This is a 13 year old camper. I do not have any instructions.
  • I have inquired of the camper manufacturer for a manual. They are only available for model years 2015 and later.
  • With the exception of one device, the AC appliances are embedded such that I cannot find a model number that would allow me to attempt finding online instructions.
  • I have found the instructions for a fridge that was added. They only say to use a grounded outlet. However, I know the previous owner ran the fridge for years off an inverter, just as I am doing.
My understanding of a ground is to provide a path for current in case of a fault. I'm only attempting to add safety. Does knowing that there is AC being supplied to a distribution panel via an inverter connected to a LiFePO4 battery not provide enough information to allow adding a proper ground, when I have access to the wiring prior to the distribution panel?
The instructions we need to follow are for the inverter.
You say the fridge requires a ground, it looks like you have no ground when running off the inverter.
Reply to Hot Neu. / Reverse when on inverter power in the DIY Electrical Advice area at ElectriciansForums.net
Thank you. I looked further into transfer switches and that will indeed work for me, and I'll only need one. Perfect. Thanks again.
Thanks again. Looking into it, it seems that the breaker panels in U.S. homes pretty much all employ 15-amp C-curve breakers for the 15-amp...