Back fusing/ Protecting a cable 2 | on ElectriciansForums

Discuss Back fusing/ Protecting a cable 2 in the Electrician Talk | All Countries area at ElectriciansForums.net

S

sparkmanuk

I postedthis question about two weeks ago,

If you have a busbar chamber supplied by a large cable fused at say 100A, and then smaller cables taken from the chamber that go to isolators that are rated at 30A. Technicaly the smaller cables are underated but, cannot pull more than their design current due to the isolators they are connected to, is this allowed by the regs, I know this is done all the time but is it BS7671.

The concensus of posts was it is allowed!, I would like to add further debate to this, by saying that if this is allowed then you could have say a 4mm swa on a 63A breaker out of a consumer unit as long as it is terminated into a fused isolator that is the proper rating for the cable, if i am correct Part p has stopped spuring off the domestic socket ring to a double socket in 2.5, since 26A could theoretically be pulled, I know part p dosent cover all industrial.

I am wondering if their is not a written rule or interperitation of another rule that lets a cable have a higher protection rating than the cable can handle, or a certain percentage higher fuse rating for a cable as long as it is terminated to a fuse isolator of proper fuse rating.

Because as an example if you have a busbar chamber protected by a 200A fuse with say a 2.5mm swa going to a 20A isolator and a 4mm swa to a 30A isolator and a 10mm to a 60A isolator, if one of the cables were to be squashed against the wall by say a fork lift or object.

Then the smaller calbles are more likey to blow on impact, so my point is the smaller the cable the greater the chance of a 200A explosion which makes me think their is either a rule of thumb or written guidence somewhere, like say steel wired armour csa to potential dead short current, and i know you could say you design the installation to the risks but the use of a factory/ installation can change.

I would welcome anyones thoughts on this.
 
I postedthis question about two weeks ago,

If you have a busbar chamber supplied by a large cable fused at say 100A, and then smaller cables taken from the chamber that go to isolators that are rated at 30A. Technicaly the smaller cables are underated but, cannot pull more than their design current due to the isolators they are connected to, is this allowed by the regs, I know this is done all the time but is it BS7671.

The concensus of posts was it is allowed!, I would like to add further debate to this, by saying that if this is allowed then you could have say a 4mm swa on a 63A breaker out of a consumer unit as long as it is terminated into a fused isolator that is the proper rating for the cable, if i am correct Part p has stopped spuring off the domestic socket ring to a double socket in 2.5, since 26A could theoretically be pulled, I know part p dosent cover all industrial.

I am wondering if their is not a written rule or interperitation of another rule that lets a cable have a higher protection rating than the cable can handle, or a certain percentage higher fuse rating for a cable as long as it is terminated to a fuse isolator of proper fuse rating.

Because as an example if you have a busbar chamber protected by a 200A fuse with say a 2.5mm swa going to a 20A isolator and a 4mm swa to a 30A isolator and a 10mm to a 60A isolator, if one of the cables were to be squashed against the wall by say a fork lift or object.

Then the smaller calbles are more likey to blow on impact, so my point is the smaller the cable the greater the chance of a 200A explosion which makes me think their is either a rule of thumb or written guidence somewhere, like say steel wired armour csa to potential dead short current, and i know you could say you design the installation to the risks but the use of a factory/ installation can change.

I would welcome anyones thoughts on this.

if the factory changes it use then a survey and risk assesment would be carried out
 

Reply to Back fusing/ Protecting a cable 2 in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
574
The total current capacity of the system in amperes is the same as the per-phase rating when referring to a balanced three-phase system. Thus, a...
Replies
4
Views
469
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
1K
The cable needs protecting the same as if a load was connected on the far end of it, rather than a generator, except that it must not share a RCD...
Replies
7
Views
2K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
670

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks