If you have a busbar chamber supplied by a large cable fused at say 100A, and then smaller cables taken from the chamber that go to isolators that are rated at 30A. Technicaly the smaller cables are underated but cannot pull more than their design current due to the isolators they are connected to, is this allowed by the regs, I know this is done all the time but is it BS7671.
 
If you have a busbar chamber supplied by a large cable fused at say 100A, and then smaller cables taken from the chamber that go to isolators that are rated at 30A. Technicaly the smaller cables are underated but cannot pull more than their design current due to the isolators they are connected to, is this allowed by the regs, I know this is done all the time but is it BS7671.

Regulation 434.2.1 applies here. It allows the reduced cross sectional area of the conductors for a distance of 3 metres.:cool:
 
No alibi what yo have to do is adjust your cable size for the upsteam fuse.
For example a 300A busbar -----> 100 hrc switch fuse protecting a d.b then you can use a 25mm cable as the fuse upsteam will blow before to much load is drawn throught the cable.

Hope that makes sense.
 
I understand the theory, but if i put the point like this, If a large factory were to be wired today by a large respected industrial contractor like 'Baileys' etc would they allow it. I am asking this question because like all sparks you look at how others have installed things over the years, but I sometimes wonder if i am picking up bad habits from old sparks.
 
I understand the theory, but if i put the point like this, If a large factory were to be wired today by a large respected industrial contractor like 'Baileys' etc would they allow it. I am asking this question because like all sparks you look at how others have installed things over the years, but I sometimes wonder if i am picking up bad habits from old sparks.


Simple answer is yes they would do it!I have seen i tdone a lot and it is legal. Just be carefull about the upstream protective device.
 

Reply to Back fusing/ Protecting a cable in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
318
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
297
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
361

Similar threads

I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
670
  • Question
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
Replies
2
Views
620
loz2754
L

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top