pushrod
I=P/U have alook at table 7.1 in the OSG . when you are designing circuits the length is not usually something that you can change.
You haven’t downloaded it then Archy? I had a look at the site and got as far as them wanting an e-mail, postal address, phone No……… I always get cold feet at that point, I just don’t like giving it out.
so what your saying is you need to know the length and then design to that.. .
You are putting a circuit in- You have worked out the likely max load and circuit breaker and cable size. Then you check the length of cable you are putting in against table 7.1 and if it it is less than the max length shown for the conditions you are using you then you should be ok for volt drop. If it wasn't ok you would think about changing the design, eg increasing the cable size or maybe dividing the circuit up etc
is that where distribution circuits come in then???? ps i ask myself more questions than i need to probably thanks.
If you are putting your new circuit in from a sub main you would have to calculate what size Vd you were getting from the main CU to there and take that figure from your 5% or 3% figure. You could not use table 7.1 for a circuit from a sub main. As the distribution circuit to the sub main will use some of your allowable volt drop.
woke up and thought more on this i think the question was calculate max length for a perticular circuit?
page 38 of my amicus 16th ed to good electrical practises states
cable length x design current x mv / A /m
---------------------------------------- = volt drop
1000
so please correct my first attempt at this,but i think using transposition of formulae thingy u could say
L = Vd
---------------- x 1000
Ib x mv/A/m
so if you know the max volt is 4 % of 230v = 9.2 volts
input your design current and cable voltage drop rating you can calculate max permitted length of cable ( this does not take into account grouping factors wirring methods etc.)
please correct any mistakes.... as its been a while and had a few cobra beers last night.
basic adiabatic equation s= root(Isquaredt)/kWhen calculating the minimum value of the cross-sectional area of a protective conductor the following information is available Fault current = 650A Operating time of protective device = 0.3s Constant k, for protective conductor material = 115 The minimum cross-sectional area of the protective conductor must be
a. 2.5mm2
b. 1.5mm2
c. 6.0mm2
d. 4.0mm2
cant figure this 1, if you want to help