growler

-
Arms
Joined
Jan 1, 2010
Messages
456
Reaction score
98
Location
Basingstoke
A customer has asked me to connect his back up generator 'properly' as currently he just flicks the main switch and plugs straight into the down stairs ring main.
I admit I have little experience with this and won't take it on unless I'm 100% I'm doing it correctly. It's a 5.5kva generator on a tt.
Can somebody help me with what I need to consider ?
So far I'm thinking
- change over switch
- earth electrode
 
Here we go.
1) your change over switch MUST disconnect Phase/ neutral AND EARTH from your DNO supply
2) Install an earth rod or mat connected to the frame of the genny
3) Link Neutral and Earth in the alternator
4) Unless the alternator has a method of maintaining the correct voltage / frequency, ie an AVR, do not connect any electronic equipment to the output
 
I will give you two other bits of advice,free. 1) your geny is of the wrong type and undersize, 2) Your customer will not pay what you will require to do it properly.....the distance between using the ubiquitous double plug top lead,and the correct system,is about the price of a month cruise to somewhere expensive...bon appetit
 
I personally wouldn't worry about disconnecting the earth, as you're always going to have inadvertent connections via bonding, CPC's and the general mass of earth, between your genny rod, and the DNO earth. In this instance, being a TT system, you needn't disconnect the earth anyway.
 
I will give you two other bits of advice,free. 1) your geny is of the wrong type and undersize, 2) Your customer will not pay what you will require to do it properly.....the distance between using the ubiquitous double plug top lead,and the correct system,is about the price of a month cruise to somewhere expensive...bon appetit

Would you care to expand on any of this?

How do you know what type of generator the OP's customer has?
Why do you say that 5.5KVA is too low for domestic backup?
Since the earthing is TT and is likely to already have adequate RCD earth fault protection, why should doing it properly cost the price of a month's cruise?
 
Here we go.
1) your change over switch MUST disconnect Phase/ neutral AND EARTH from your DNO supply
2) Install an earth rod or mat connected to the frame of the genny
3) Link Neutral and Earth in the alternator
4) Unless the alternator has a method of maintaining the correct voltage / frequency, ie an AVR, do not connect any electronic equipment to the output


Why would you need to disconnect the DNO earth, come to that,...how would you??
 
You can’t rely on the DNO earth as work could be ongoing on the LV system. But as this is TT it’s not a problem.
As Phil has said a positive change over is needed for both L&N.
Linking N&E makes the installation when running on the generator TN-S.
 
Why would you need to disconnect the DNO earth, come to that,...how would you??

During a power outage, you cannot assume the DNO's earth is intact or your own earth rod. Theres also the possibility that the genny will send a voltage down the DNO earth.
The 2poles and earth go to the 'Mains' side of the change over switch / contactor before going to the DB.

- - - Updated - - -

You beat me to it Tony
 
During a power outage, you cannot assume the DNO's earth is intact or your own earth rod. Theres also the possibility that the genny will send a voltage down the DNO earth.
The 2poles and earth go to the 'Mains' side of the change over switch / contactor before going to the DB.

- - - Updated - - -

You beat me to it Tony

What are you saying, ...that a 3 pole C/O switch is needed for a single phase supply??
 

Reply to Back up generator on domestic in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
856
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top