Customer has already acquired a 'Loncin 80000-F' 6kW generator which has 115V and 230V sockets, to be used to run a few lights and central heating in power cuts. They are T-T. Genny also has a circuit breaker of sorts.
I'm suspecting it is not suitable as it will have a floating earth, chassis connected to the center point of the winding, meaning it will need double pole protection. Would it be acceptable to attach an earth electrode to the chassis then take the supply from the genny into an enclosure where the earth and neutral are linked and then Live & Neutral passed though an RCD, then a suitable MCB, then take the supply into a manual changeover switch?
I'm suspecting it is not suitable as it will have a floating earth, chassis connected to the center point of the winding, meaning it will need double pole protection. Would it be acceptable to attach an earth electrode to the chassis then take the supply from the genny into an enclosure where the earth and neutral are linked and then Live & Neutral passed though an RCD, then a suitable MCB, then take the supply into a manual changeover switch?