Went to replace a 4 way Wylex consumer unit today. Easy peasy - wrong!
When dismantalling the CU was testing as I went, on ring r1 was approx 300 ohms, rn around 600 ohms. Spent some time trying to find the problem without raising floorboards etc. and the problem seemed to be between the CU and 1st/last socket, so was about to disconnect that leg and make it a radial. I then did the insulation test - dead short between neutral and earth!
Couldn't find it, I know where it is in the general area near a bedroom socket, but floor is over boarded!
Had to re-assemble CU. Back tomorrow, couldn't access another nearby socket behind wardrobe so customer moving it tonight, for me to have another go!
Previous owner was a DIYer, other issues need sorting as well!
This is the 2nd installation in 2 weeks were a DIYer has caused problems!
When dismantalling the CU was testing as I went, on ring r1 was approx 300 ohms, rn around 600 ohms. Spent some time trying to find the problem without raising floorboards etc. and the problem seemed to be between the CU and 1st/last socket, so was about to disconnect that leg and make it a radial. I then did the insulation test - dead short between neutral and earth!