timhoward

-
Broke Internet
Esteemed
Arms
Supporter
Joined
Jul 19, 2019
Messages
4,626
Solutions
1
Reaction score
9,852
Location
Oswestry
Two lighting circuits covering various communal areas on two floors of a HMO.
The non-maintained emergency lighting that covers those areas is on a separate circuit (actually with the fire alarm). So either of the lighting breakers could trip and the relevant lighting wouldn't come on.

Who takes the view that this is a NOTE as it's not an electrical safety issue, and who takes the view that the electrical installation was badly thought out and/or implemented and it's fair game to code this as an electrical issue? My leaning is the former. Who's on which side of the fence?!

As far as I can see the only trivial improvement is putting the maintained links in them all.
 
What do their rating plates state X 1 180 or X 0 180.
Sorry I didn't notice. All I can say is that they are elderly Eterna units (pre-LED) with the choc-block style connection. They are in all likelihood overdue replacement anyway.
I don't claim to be a BS5266 expert which is why I'm asking here - my understanding was that the current arrangements aren't compliant. As ever I'm happy to be corrected though. Ultimately I'm trying to provide helpful and accurate advice to a landlord.
 
That leaving them on 24hrs or can the L be switched (or tested)?
I'm actually starting to have doubts now that these fittings are able to be maintained after all.

At the moment if the lights go off due to a breaker trip the emergency lights won't come on.
This is because they are wired via test switch from another circuit (which is shared with the fire alarm, another issue...)
Future options as I see it are
a) rewire them to be on the relevant circuits
b) mess around with contactors from both the circuits which seems overkill and adding parts to maintain and replace.
c) have the emergency lights on all the time ( which occured to me while driving back and may in fact not be possible with the current fittings)

But I'm mainly interested in whether it's appropriate for this to be a C3 or C2 as opposed to a Note (as per expired smoke alarms etc)
 
If they are the old Eterna 8w tube fittings they are either M or NM and NM cannot become M. NM fittings must operate upon failure of the local general lighting.
Personally I wouldn't mention it in the Report they should be routinely tested and if this is done by a competent person they should be noting this.
The fire alarm should be a dedicated circuit wired in FP200 or equivalent and should not have anything else connected from it.
 
I'm actually starting to have doubts now that these fittings are able to be maintained after all.

At the moment if the lights go off due to a breaker trip the emergency lights won't come on.
This is because they are wired via test switch from another circuit (which is shared with the fire alarm, another issue...)
Future options as I see it are
a) rewire them to be on the relevant circuits
b) mess around with contactors from both the circuits which seems overkill and adding parts to maintain and replace.
c) have the emergency lights on all the time ( which occured to me while driving back and may in fact not be possible with the current fittings)

But I'm mainly interested in whether it's appropriate for this to be a C3 or C2 as opposed to a Note (as per expired smoke alarms etc)
Seems like DIY.
Emergency lighting is a different test procedure and certificate than an EIC or EICR, so I think it would be a notation rather than a C2 or C3, if anything.
 
You say if the breaker trips the E/M lights won't come on.
Are they not battery operated for power loss?
He means if either of the lighting circuits trip they won't come on because they are wired through another circuit.
 
560.9, any emergency lighting should comply with the relevant parts of BS 5266/BS EN 1838. If it is designed/installed in such a way that it doesn't perform as it should then it can't, by extension, be deemed to meet the parts of 5266-1/1838.

Really you want to see how it was designed as it could be fundamentally flawed, in which case a case could be made under the Fire Safety (Regulatory Reform) Order 2005 and statutory breaches could be present but that is really for the licensing authority.

Whether to C2/C3 is would be personal choice, being a safety service I would want it fixed so would C2 it, moreover being a HMO it may have additional stipulations from the licensing authority, given more weight to a code of C2 over C3.
 
Two lighting circuits covering various communal areas on two floors of a HMO.
The non-maintained emergency lighting that covers those areas is on a separate circuit (actually with the fire alarm). So either of the lighting breakers could trip and the relevant lighting wouldn't come on.

Who takes the view that this is a NOTE as it's not an electrical safety issue, and who takes the view that the electrical installation was badly thought out and/or implemented and it's fair game to code this as an electrical issue? My leaning is the former. Who's on which side of the fence?!

As far as I can see the only trivial improvement is putting the maintained links in them all.
Not an expert on em lighting,but could a contactor on each lighting cct with series contacts break the cct to the em lights if any lighting cct failed?
 

Reply to Bad emergency lighting install in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
707
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
Or a combined fitting in each row.
Replies
19
Views
2K
nicebutdim
N
  • Question
Anywhere where the normal lights are dimmed or dimmable the emergency lighting should be of the maintained type. So maintained emergency lighting...
Replies
4
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top