If the conduits are in the walls as drops only and not grounded in any way and are not in contact with any extraneous conductive parts or exposed conductive parts then should be fine and no need to earth conduits.
 
stevieh, ive seen them all, wooden pattresses with surface switches, wooden flush boxes with flush switches, we used to re use these boxes and fix plate switch with chrome 6s woodsrews, of course not advisable now (FLAMMABLE BACK BOX), ive also seen wooden trunking underfloors slotted for single v.i.r. cables in them, with a flat lid, must have been a joiners job to install the trunking it was a work of art. So re-use those metal conduits and extend with capping, its not a problem, but dont forget your zoning.
regards dave
 
I presume the reason you have mentioned the 17th in the post is because of the rcd requirements.

So can you run in the conduit. Yes of course you can.

Does it absolve you from puting the lights on a 30mA? No

so, just run the cables in as if it was a chase and put on an RCD, or earth the conduit and dont protect with RCD - both ways would meet the regs.
 

Reply to Bad practice or fine ? in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
644

Similar threads

And if it's a garage then use metal clad accessories.
Replies
5
Views
406
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
2
Replies
21
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top