The supply is PME which initially made me think that it could be broken PEN but tested and it seem's fine.
Hot tub wired in armoured all the way. Plastic board. Armoured glanded into box above CU. Earth on sheath wasn't earthed but have put that right today.(was picking up about 50-60v off the sheath.) Induction most likely. Armoured run is about 15m from the house into a rotary isolator. Isolator look's ok. Zs seemed within normal range if slightly higher than expected. They have spurred off the hot tub supply to feed some light's in the decking. (fused spur next to rotary iso) which made me think could that be anything to do with it (bit dodge). DIdn't even start looking at the hot tub itself. Just wanted to confirm it wasn't the wiring before calling an engineer out. Was debating putting an earth rod in but will see what the engineer says first. In the hot tub itself the armoured is just in a cord grip no gland needed wouldn't know where to start with pump's ,heater etc.