At ÂŁ73 I wouldn't call them free :lol:Yeah but you get 8 free drinks after that!
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Basic safe isolation question. in the Electrical Course Trainees Only area at ElectriciansForums.net
At ÂŁ73 I wouldn't call them free :lol:Yeah but you get 8 free drinks after that!
Well down here in Bath, a pint is in excess of ÂŁ4 in most places. A good deterrent though i guess for staying away from the pubs.
Over ÂŁ4 just in a local bar? that is a little pricey
Yep, For instance the pub local to me sells a pint of Heineken for ÂŁ4.30p.
In Bradford city centre pints can be around ÂŁ4, ÂŁ3.60 in one place if I remember correctly but usually I go to all the little sh**holes. but most pubs here are around the ÂŁ3 mark so it's not too bad. Acapulco in Halifax... 75p drinks(until 11:30 then they get ridiculously expensive)Yep, For instance the pub local to me sells a pint of Heineken for ÂŁ4.30p.
wow. Did not expect that. Suppose I'll have to show up to work tomorrow... Well later. Those big shot companies always s**t on the little guys. Ruined my million pound idea *sob*Aaaaaaaand here you go, a battery powered coffee machine, you asked, makita provides!
hahahaha
Makita UK
Thanks Pete, Archy I've been studying the safe isolation procedure.
I'm pretty sure most of it has sunk into my thick skull
I'm asking the main live feed to the Consumer is still live.
I was getting a reading with my voltage tester telling me it was live.
You don't have a thick skull!You are a trainee, you are asking because you don't know, this is normal, and it is the right thing to do. Those with the thick skulls have all been killed or injured because they didn't find out and guessed wrong.
Anyway you asked so i will give you the correct way.
Identify circuit to be isolated.
Switch off circuit (Trip breaker/pull fuse).
Fit a suitable isolation device and lock off
Using an approved voltage indicator and proving unit.
Prove voltage indicator with proving unit, it should light up.
Using voltage indicator test each pole to every other.
3 steps if single phase L-N, L-E, N-E
6 steps if 3 phase no neutral L1-L2, L1-L3, L2-L3, L1-E, L2-E, L3-E.
10 steps if 3 phase and neutral. Same as 6 step plus these 4.L1-N, L2-N. L3-N and N-E.
Voltage indicator should not light.
Reprove voltage indicator with proving unit it should light up.
You have now completed "Safe Isolation" to the standard required under the Electricity at Work Regs.
A known live supply can be used if you don't have proving unit.
If you don't have a voltage indicator and proving unit, then buy one.
You cannot use a multimeter of any kind to carry out safe isolation for 2 reasons. It is not the correct instrument because it is not a Voltage indicator, and it can be selected to the wrong range or setting, which can lead to interpretation of wrong results and you getting it all up your arms.
if you don't safely isolate properly, you can and will get prosecuted if you get a shock and live to tell the tale. You will be asked some awkward questions from people who you would rather not be interviewed by, the local A&E wont think you are clever, and you certainly wont be laughing about it in the pub, but the local undertaker may thank your family for the business....
It isn't rocket science but it needs to be done right.
Enjoy.