called to a job where the customer wanted more sockets in his bedroom. more than surprised to find a bath about 1 meter away from his bed which he said was moved there 12 years ago with the full consent of the council.he said they hadn't brought up any problems with existing sockets when this was agreed.told him he can't have any sockets within 3 meters of bath.he said he can't accept that.he's also got light switches in the room. would i be right in thinking that's not on also?they're also within 3 meters of the bath
 
As markc123 said, don't get involved unless he is willing to toe the line of the regs.

If there are sockets already within the 3m zone I would be walking away and issuing a letter to the client detailing the dangers involved. Any RCD protection present on existing sockets ?
 
With that bath there that bedroom has become a "special location" in the regs! Any work you do has to comply to the 3m distance, RCD etc ..... so you CANNOT be adding to the existing socket circuits. You can add sockets in the location provided they are greater than 3m and on a new circuit plus meet all the other requirements -- but not off the existing socket circuit in the bedroom.

Dont forget on the EIC for the new circuit, you would also have to raise the non-conformance of the existing sockets and possibly issue a report of a potentially dangerous situation depending on how you view it!

Think the best advise has been given above. If the customer doesnt want to change then pack up your tool bag and head for the nearest door!
 
With that bath there that bedroom has become a "special location" in the regs! Any work you do has to comply to the 3m distance, RCD etc ..... so you CANNOT be adding to the existing socket circuits. You can add sockets in the location provided they are greater than 3m and on a new circuit plus meet all the other requirements -- but not off the existing socket circuit in the bedroom.

Dont forget on the EIC for the new circuit, you would also have to raise the non-conformance of the existing sockets and possibly issue a report of a potentially dangerous situation depending on how you view it!

Think the best advise has been given above. If the customer doesnt want to change then pack up your tool bag and head for the nearest PUB![/QUOTE]

I have corrected your mistake.

There will be no charge for this.
 
Still struggling to justify a bed next to the bath...

EUREKA

Has the Client installed it for those times his wife is snoring at 4am when you're up at 6 so he can shove her off and nearlly drown her to get her to SHUT THE F UP!!!!!!!!

? :)
 
Still struggling to justify a bed next to the bath...

EUREKA

Has the Client installed it for those times his wife is snoring at 4am when you're up at 6 so he can shove her off and nearlly drown her to get her to SHUT THE F UP!!!!!!!!

? :)

Sorry about that ... I had a particularly bad curry last night.

I can lend you a can of air freshener until such times as my vowels return to normal.
 
called to a job where the customer wanted more sockets in his bedroom. more than surprised to find a bath about 1 meter away from his bed which he said was moved there 12 years ago with the full consent of the council.he said they hadn't brought up any problems with existing sockets when this was agreed.told him he can't have any sockets within 3 meters of bath.he said he can't accept that.he's also got light switches in the room. would i be right in thinking that's not on also?they're also within 3 meters of the bath

You need to brush up on your zones.
 

Reply to bath in bedroom in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
310
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
935

Similar threads

I have an "old school" electricity monitor similar to this one...
Replies
3
Views
156
The challenge that you have with this is that you've no confirmed start point. Because you have a lack of an EICR you don't actually know what...
Replies
7
Views
589

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top