R

Richard Redman

Hi all, after some advise on bonding in a bathroom, ive fitted an electric shower, its RCD protected and ive bonded the water pipes. 2 of the walls in the bathroom are steel stud walls, another electrician says it doesnt need bonding as its on a RCD ? Help
 
Brilliant, thats cleared the conflicting views ive had, cheers Ian .
Also on the subject of bathrooms, the light in the bedroom from which i want to take a feed from for bathroom lighting has been run in twin no earth and the lights im fitting in the bathroom are ipx4 plastic fittings . What would be the best option here ?
 
dispite being plastic are they class 2 equipment or do they have internal parts like metallic gear tray which requires a earth?

Generally the regulations require a cpc to be ran to each point of the electrical circuit apart from suspended bayonet lamp holders forming a standard ceiling rose.
 
Initially, i was going to run from the bedroom light to a swtchrd fuse spur and then run my two new bathroom lights and extractor fan, but now ive noticed this bedroom light has no cpc .
I'll be using 1.5t&e, but i have no earth to connect to and borrowing an earth isnt good practise !
 
Initially, i was going to run from the bedroom light to a swtchrd fuse spur and then run my two new bathroom lights and extractor fan, but now ive noticed this bedroom light has no cpc .
I'll be using 1.5t&e, but i have no earth to connect to and borrowing an earth isnt good practise !
so feed your SFCU ( 5A or 3A if fan instructions call for 3A ) from a local socket circuit. label in the CU that the bathroom lights and fan are supplied from MCB --- via FCU with the FCU location.
 
do all the lights have no cpc to them?
Can you install a new supply to the bathroom lighting from the DB?
What happened to the existing wiring to the bathroom lighting?
Is this a newly built room? If so you've installed a shower so just install a new supply.
 
This is an en suit to the bedroom , so the light for the room will remain in the bedroom , so need to fit lights in the bathroom.
I dont have enough room in the c/u to fit a another cb . This seems to be the only light in the house without a cpc.
The closest socket i was going to use to feed an electric towl radiator via a sfcu, could i run lights, fan and radiator from the sockets via a sfcu ??
 
So, after reading through these feeds, am i understanding that a steel stud wall in a bathroom is an extraneous part, which doesnt need bonding as all the circuits in the bathroom are RCD protected?
Thanks for the advise on this, ive conflictincting views from other sparks, which has made me dout my own knowledge of whats an extraneous part or not.
I think it comes down to years ago they use to make you bond everything and the kitchen sink! But systems hsve changed, and RCD's are in play now.
Its an older type plastic c/u but ive arranged it so that all circuits are RCD protected except for down stairs lights, as not enough room on that side, so all circuits upstairs and the bathroom are protected.

You'll need to think on that, otherwise you are non compliance on division of installation reg 314.
 
Initially, i was going to run from the bedroom light to a swtchrd fuse spur and then run my two new bathroom lights and extractor fan, but now ive noticed this bedroom light has no cpc .
I'll be using 1.5t&e, but i have no earth to connect to and borrowing an earth isnt good practise !

Think you need to take step back and draw breath, and reconsider your addition/alteration.
 
This is an en suit to the bedroom , so the light for the room will remain in the bedroom , so need to fit lights in the bathroom.
I dont have enough room in the c/u to fit a another cb . This seems to be the only light in the house without a cpc.
The closest socket i was going to use to feed an electric towl radiator via a sfcu, could i run lights, fan and radiator from the sockets via a sfcu ??
Choose another upstairs light to come off?
One with a cpc.
Install a new mains and double up with existing upstairs lights, this will be one circuit after all.
 

Reply to Bathroom bonding with steel stud walls in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

Similar threads

  • Question
If there's no main switch on the CU, then the RCD is doubling up as the main switch and everything is protected by it. If there is a main switch...
Replies
5
Views
765
  • Question
ok cheers for the help lads
Replies
7
Views
708

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top