So what has changed in the 17th that specifically affects the decision to not bond in the bathrooms now? Is it because bathrooms have to be on SELV or RCD/RCBO now or is it because the powers at be have just decided its no longer neccesary as long as incoming supplies are bonded...in which case what has changed as incoming was a necessity under the 16th.:confused:

Btw..nice write up jurassaic;)
 
So what has changed in the 17th that specifically affects the decision to not bond in the bathrooms now? Is it because bathrooms have to be on SELV or RCD/RCBO now or is it because the powers at be have just decided its no longer neccesary as long as incoming supplies are bonded...in which case what has changed as incoming was a necessity under the 16th.:confused:

Btw..nice write up jurassaic;)

under 17th:

no supplemntary if all circuits in bathroom ona 30mA RCd (which they must be), meet their disconnection times, and extraneous conductive paths of resistance of 1667 ohms or less to MET/Protective bonding

Lets be honest there are few extraneous paths in a modern bathroom anyway because of plastic piping
 
Is it important that the wire isn't broken? I'm installing supp bonding in care homes at the moment, and I have been cutting the wire when installing, and connecting it all up at the points of contact eg cold pipe, rad.
 
Is it important that the wire isn't broken? I'm installing supp bonding in care homes at the moment, and I have been cutting the wire when installing, and connecting it all up at the points of contact eg cold pipe, rad.

dont see why supp's have to be unbroken

I know it does with main bonds if you are running one cable out to gas and water, but supp's, you are not running a cable back, just connecting together extraneopus and exposed - so each bond is an entity in its own right - I can see no advantage of having an unbroken cable (and I have never heard of it)
 
under 17th:

no supplemntary if all circuits in bathroom ona 30mA RCd (which they must be), meet their disconnection times, and extraneous conductive paths of resistance of 1667 ohms or less to MET/Protective bonding

Lets be honest there are few extraneous paths in a modern bathroom anyway because of plastic piping

Thanks shakey for the explanation, does this mean selv on rcd is a must also, for the cable's protection? only if using a pull switch then no cables will be in the wall (less than 50mm) so am still a little confused to why rcd is needed for bathroom selv lighting
(or maybe i'm just having an elderly moment lol):eek:
 
Thanks shakey for the explanation, does this mean selv on rcd is a must also, for the cable's protection? only if using a pull switch then no cables will be in the wall (less than 50mm) so am still a little confused to why rcd is needed for bathroom selv lighting
(or maybe i'm just having an elderly moment lol):eek:

hey old fella:p

apart from the requirements for cables buried less than 5 cm, there is a requirement that all circuits in the bathrom are on an RCD
 

Reply to Bathroom Bonding in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
454
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
946
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
895

Similar threads

Hi all, first post, please be gentle ;) Iv been involved in a bathroom refurb, nothing major, moving a light fitting and switch. My problem came...
Replies
0
Views
293
  • Question
The chances of any problem without the RCD are minimal, including it extremely negligible......with the supplementary, on a kin to Hannibal Lector...
Replies
6
Views
840

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top