They’ve already got a name….Fair point. I think from now on we use use the term EICR Monger for anyone producing dodgy ones.
“Drive-by-ers”
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Bathroom Down-lights CODE C2? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
They’ve already got a name….Fair point. I think from now on we use use the term EICR Monger for anyone producing dodgy ones.
They are outside the zone but as you and DPG state to stop the ambiguity why didn't they put 2.5 metres as the majority of houses are 2.3m. They put it under 8.6 Suitability of equipment for external influences for installed location in terms of IP rating and 8.7 Suitability of equipment for installation in a particular zone. They aren't rusty & there is no deterioration as they were only fitted (by a bathroom fitter & team) 3 or 4 years ago. They are RCD protected. It wasn't an inspector just an approved contractor. I didn't particularity want some some shiny new down lights to be honest but it looks like I have to as they err'd on the side of caution .. and I know you can have a light switch 60cm from the edge bath or shower but I guess I could still become a monger : )I've always thought the zone height was a daft one - in most houses downlights are usually just outside the zone, and therefore not required to be a particular IP rating.
Would have made more sense to make it to the ceiling, or set a height more than the average house ceiling (2.5m maybe) . It's not like steam stops at 2.25cm!
@brianmoooore is correct in that if they have given it a C2, it should be under "suitability of current-using equipment for particular position with the location (701.55)", rather than "suitability of accessories and controlgear etc. for a particular zone (701.512.3)"
Or it could go under "Suitability of accessories for external influences (512.2)" I guess.
I'd feel C3 would be more appropriate though tbh, unless they are rusty. They are presumably RCD protected anyway, and if you are tall enough to change bulbs while in the shower and do so then not sure an EICR is going to save you!
Was it a NAPIT inspector? Could be the NAPIT guide striking again and someone not using actual judgement. (Don't have a copy to check what they say)
It's a common code I saw with the quicky EICR mongers that popped up to fill the PRS need - They no doubt wanted to sell some shiny new downlights.
Maybe the same ones who will swear blind you can't have a light switch in a bathroom, or that there is a zone around a sink.
Hi Brian thanks and hopefully answered above.The C2 should quote the number of the reg that has been violated. If it's the one referring to zones, then the classification is incorrect; if it's the suitable for environment one, then maybe C2.
Hi Spoon assumingly they are not IPX4 otherwise he wouldn't have regarded it as a C2 and in terms of zoning they aren't in a zone. As said it looks like I'm the victim of erring on the side of caution but hey ...Nope, nothing has changed with regards to zones.
So what IP rating is your light and what zone is it in?
Hi Brian they C2'd items 8.6 & 8.7 in Part 10 and to give you the exact wording in Part 6 ... '8.6 Down Lights (x2) above bath not of correct IP rating' which is exactly the same as the next item '8.7 Down Lights (x2) above bath not of correct IP rating'. I did try to challenge via email but to no avail hence me coming on the forum for advice. I guess it could come under 8.6 but as said they aren't rusty & there is no deterioration so I guess as Loz states is a judgement call which I will abide as it makes sense I guess. Regards AlanIf they mentioned 'zone' and not preceded by 'outside of', then the classification is wrong, and should be challenged. The lights are not in a 'zone'.
They may still classify it as a C2, but not for any reason that makes reference to zones.