Called to quote for installing some IP rated down lights in a bathroom. Told guy he needed an RCD for altering light etc and he wasnt pleased. Some old un-named mcb's in his C.U so i told him either a seperate 1 way c.u would do it or a new C.U all together to bring it upto date. Nope didnt want it :( Why do people think its just put that there and off you go..... Grrrr

Anyways i was thinking, could a RCD Spur be fitted outside the bathroom (above door etc) to feed the new lights in the bathroom, would this do?
 
your more than capable of deciding wether the circuit can meet disco times and handle additional loading, and also capable to decide wether an inline rcd would cover the part of the installation being worked on or wether it would need you to install additional protection upstream.

as the electrician the buck stops with you, you make your decision on the installation.
 
Last edited by a moderator:
To comply with BS7671 all circuits in a domestic bathroom need to have additional protection by a 30mA rcd. The normal way is to introduce the device(s) in the consumer unit. This can be achieved however in other ways eg rcd spurs etc. If all circuits are covered with rcd protection, main bonding has been carried out, and earth fault loop results are acceptible for all bathroom circuits then supplementary bonding may be omitted in the location.
 
Hi there, That sounds good to me, however I’m still not sure about RCD spurs to feed lighting installed in a bathroom, You still need to provide RCD protection to the circuit feeding the spur if its buried less than 50 MM in the fabrication of the building. Eg most domestic properties, unless you can confirm it has sufficent mechanical protection.
Regards KJ

 
 
Not so. If it's an existing circuit this will be to the old reg's, And the only requirement is to protect the part of the circuit you worked on via an RCD, So an RCD spur unit is fine as long as you cross bond and the main bondings in place.
 

Reply to Bathroom lights RCD etc in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
145
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
944
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
490
  • Question
ok cheers for the help lads
Replies
7
Views
816

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top