Bathroom lights RCD etc

T

timo

Called to quote for installing some IP rated down lights in a bathroom. Told guy he needed an RCD for altering light etc and he wasnt pleased. Some old un-named mcb's in his C.U so i told him either a seperate 1 way c.u would do it or a new C.U all together to bring it upto date. Nope didnt want it :( Why do people think its just put that there and off you go..... Grrrr

Anyways i was thinking, could a RCD Spur be fitted outside the bathroom (above door etc) to feed the new lights in the bathroom, would this do?
 
people think that we take them for rides and that gear costs us 20p for a job load..!! Walk away from it,

RCD spur = £25
cheap RCBO = £13 with £2.00 enclosure plus cable... probably cost same price, what suggests he will not want to pay for the RCD spur either...!

its a notify job as well...! let some cowboy do what he wants and chase bigger fish mate!!
 
Last edited by a moderator:
people think that we take them for rides and that gear costs us 20p for a job load..!! Walk away from it,

RCD spur = £25
cheap RCBO = £13 with £2.00 enclosure plus cable... probably cost same price, what suggests he will not want to pay for the RCD spur either...!

its a notify job as well...! let some cowboy do what he wants and chase bigger fish mate!!

Would you need rcd on lv downlights
 
regs say RCD in bathroom ( zoned areas )

Regulation 701.411.3.3 now requires that additional protection shall be provided for all circuits of the location by the use of one or more RCDs having the characteristics specified in Regulation 415.1.1. This is a significant change. Previously (601-09-02), only
fixed current using equipment (other than electric showers) located in zone 1 required 30mA RCD protection and current using equipment (other than fixed current using equipment – such as a washing machine, if suitable for use in a bathroom, connected through a fused connection unit) in zone 3 required 30mA RCD protection. Regulation 701.411.3.3 means that all circuits, including lighting, electric showers, heated towel rails, etc., will require RCD protection, not exceeding 30 mA.
 
Last edited by a moderator:
regs say RCD in bathroom ( zoned areas )

Regulation 701.411.3.3 now requires that additional protection shall be provided for all circuits of the location by the use of one or more RCDs having the characteristics specified in Regulation 415.1.1. This is a significant change. Previously (601-09-02), only
fixed current using equipment (other than electric showers) located in zone 1 required 30mA RCD protection and current using equipment (other than fixed current using equipment – such as a washing machine, if suitable for use in a bathroom, connected through a fused connection unit) in zone 3 required 30mA RCD protection. Regulation 701.411.3.3 means that all circuits, including lighting, electric showers, heated towel rails, etc., will require RCD protection, not exceeding 30 mA.


All parts of the location not just the zones.
 
So id be ok just to spur the new lights and leave the rest of the light circuit as is?

Still would test all the light circuit out etc but only my work in bathroom would be rcd from the spur and comply ?

ta
 
Not so, the feed from the consumer unit to your lights in the bathroom will all so require RCD protection, if they are less than 50 mm buried into the fabric of the building.
Assuming you have all so confirmed bonding ECT.
Regards KJ

 
Not so, the feed from the consumer unit to your lights in the bathroom will all so require RCD protection, if they are less than 50 mm buried into the fabric of the building.
Assuming you have all so confirmed bonding ECT.
Regards KJ

They are existing and not new keith. Only thing i will be changing is the bathroom light to 4 down lights.
 
Hi there, You have to conform to, to days regs if you are installing any new equipment eg bathroom lights, you have to bring the circuit you are working on and the bonding at the Origen up to today’s standards.
Regards KJ

 
depends on how you interprit the regs and has been argued before, as you are only concerned with the bath light, then i wouldnt worry about using rcd spur to protect that part.
 
Hi there, When you alter an existing circuit, you have to confirm the circuit can supply the addition load, and subsequent fault currents, there for you have to test the hole circuit, and confirm it complies to current regs,
Regards KJ
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
timo,
Last reply from
shagg,
Replies
19
Views
12,360

Advert

Back
Top