Whist looking up something unrelated in section 701, I noticed reg 701.753
Stating that underfloor heating wire in a bathroom must have an earthed sheath or metallic earth grid etc etc & that electrical separation shall not be used
It got me thinking, the underfloor heating wire I used in my conservatory has no earth and is double insulated (different version in the bathroom).
Although I don't have an issue I am wondering if someone was to find underfloor heating in a house whilst doing a repair or an EICR or whatever and It was in a bathroom / shower room , and there was no earth conductor present or evidence to suggest it has an earth mesh, sheath or enclosure. What would you do as I can imagine if you tell the client you need to remove the bathroom floor I doubt that would go down well, and as the reg states using an isolation transformer is also not allowed?
Hi, I’m a simple person and so if I’m doing a Report, I report what I find :) .
Double insulation isn't normally considered as a means of protection in a dwelling so this is an interesting question. Why don't you email the manufacturer.
I'm not sure how you would go about ascertaining whether a mesh has been installed or not. You can only inspect what you can see.
If there was no earth on the ufh cable and no mesh and it’s within Zone 2 then the only fix I can think of would be to decommission it, sorry. Hopefully someone has another thought …
Dont be sorry, I dont have this problem my bathroom UFH has earth
was just question i wall mulling over and trying to work out if there could be any other solution, as you say probably not
I find that "double insulated" accessories are becoming increasingly problematic from a testing(EICR) point of view. It's sometimes difficult to know if you have discovered an unearthed appliance or simply found a "double insulated" appliance. "Double insulated" appliances can look just as "metallic" as their class 1 cousins. Just today I brought home a metallic "double insulated" downlighter removed from an install to add to my growing collection of "baffling" "double insulated" accessories.
Does zone 2 extend to beneath the floor?
Hi - no, but my interpretation of Reg 701.32.1 (last paragraph) is the heating mat being part of the floor means the zone requirements apply. Just my opinion and I am extending beyond what is written, as the reg only states this for walls and ceilings.
If we weren’t in a bathroom then 753.411.3.2 says Class 2 mats may not require the extra metal grid / mesh.
Reply to Bathroom UFH earth mesh in the Electric Underfloor Heating Wiring area at ElectriciansForums.net
There is no reason for an item of fixed equipment to be on its own dedicated circuit just because it is fixed equipment. There may be other...
loz2754
L
Recommended Sponsor News
thanks for the clarification. ( also thanks to Dan. ).
More info on link below http://sbsc.uk.net/
9K
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
6K