Guys
Quick question regarding moving my bathroom pull cord to a switch.
I was measuring my bathroom zones as per 7671, and I would like to put a light switch 0.73m outside of zone 2, the problem is I could not see anything relating to a light switch in particular only a socket, And pull cord switches.
All the circuits are RCD protected.
The OP's concerns are about whether a wall switch outside the zones in a bathroom is against the regs and/or unsafe.
The correct answer to that must be that it is allowed and it is not inherently unsafe. It could be safer of course through the use of pull switches or wall switches outside the bathroom, but the choice is down to the installer as to what the likely external influences are and whether the products used are appropriate.
There are examples in BS7671 that gives guidance as to what is allowed or permitted. It does not give guidance as to what is safe or unsafe.
I note from section 701, there is a description of zones 0, 1 & 2 and what and cannot be installed in those zones. There is no such guidance as to what or should not be installed outside of these zones, except 'socket-outlets are prohibited within a distance of 3m horizontally from the boundary of zone 1. There is no other guidance for what can be installed outside of these zones in locations containing fixed bath (etc) or shower, other than it does not apply to switches & controls which are incorporated in fixed current-using equipment for use in that zone or to insulating pull cords of cord operated switches.
Therefore one could install a plate switch outside of zones as it does not appear to contravene any regulation within BS7671. But that ordinary plate switch could be operated by someone stood in the bath or shower.
So IMO, 'the correct answer to that must be, that 'it appears that' it is allowed, but it is inherently unsafe'.
I obviously disagree :)
But then it's not me you need to convince, that would be the IET.
Their guidance is:
Section 701 does not specify any additional ingress protection requirements beyond zone 2. This means that accessories, such as switches and fused connection units, can be installed beyond zone 2, subject to the requirements of Regulation 512.2 (external influences).
(Taken from IET wiring matters issue 53)
The issue of considering external influences outside of zones has already been mentioned in this thread.
Like I said, it's down to the installer to assess each installation and use their judgement.
Would I fit a plate switch in a bathroom in every instance when asked ? Nope.
Have I got switched accessories in my bathroom at home ? Yep.
Could I code accessories in a bathroom fitted in accordance with BS7671 on an EICR ? Nope.
Their guidance is:
QUOTE]
One of these then :)
In my bathroom I have got a triple pole fan iso that is directly above the bath at a height of 2.29m or thereabouts. My bathroom gets cold in the winter, really cold. So I often turn the fan on just as I am getting out of the shower. It's also pretty damn steamy as well until it clears. I have never had the slightest tingle from this switch in over 14 years. I do actually intend to relocate this particular switch at some point as I have never been that impressed with its position, and I would not fit any switch directly above the bath in this way despite it being technically outside of zone 2. But I would and will continue to fit plate switches outside of zone 2 horizontally if the customer so wishes. Traditions do change over time...
Did a Periodic a couple of months back at a commercial premises and the male/female toilets had been knocked into one to create a shower room/toilet. No rcd protection on the shower or any of the circuits, an existing hand drier point is now for a hair dryer which is in zone 2 adjacent to the shower cubicle. The hair dryer is a standard appliance which you can actually use in the cubicle.
Job had just been completed, spoke to the powers that be who went ballistic on the phone to the contractor.