Beast of a cooker | on ElectriciansForums
Guest viewing is limited
Discuss Beast of a cooker in the UK Electrical Forum area at ElectriciansForums.net
B
brizospark
OK I know this has already been covered but I have been asked to install a supply and isolation switch to a Rangemaster cooker which has a rating of 14kw.
This cooker has a couple of ovens and grills and induction hobs - it's a beast
My question is regarding the cable / isolation switch rating, I know there is some debate over the issue but I reckon being realistic there is no chance that the cooker will ever run at full capacity and that a 6mm cable covered by a 40a MCB (only 5m run from board no insulation under floor) and a 45a DB switch would suffice.
The other option would be a 63a MCB with 10mm cable and a 63a rotary isolator.
The house is occupied by a couple and soon to be baby.
What would you guys do in this situation?
I know that diversity is applied for a cooker circuit, but what happens at Christmas for example, when she is running full tilt?
Do you ever think that all parts of the cooker will be drawing current simultaneously? considering thermostat control. And even if they did how long would it be for?
I have put these on 40A supplies no problem in the past.
What does the manuf recommend in their instructions?
You can use whatever C/B & wiring combination you want as long as the C/B covers the wiring --- at worst the C/B will just keep tripping on overload or the wiring will melt down if on slight overload conditions on a 24hr hog roast!!
The Rangemaster instructions with the cooker do not specify a cable/breaker size, however, when your shiny new expensive cooker goes wrong and can't be fixed in the "field", and Range Master are confirming delivery of the replacement unit, the paperwork they send, stipulates a minimum 6mm cable with a 32A MCB - I know this because it happened to us in January!
Reply to Beast of a cooker in the UK Electrical Forum area at ElectriciansForums.net
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Recommended Sponsor News
Hi everyone,