OK I know this has already been covered but I have been asked to install a supply and isolation switch to a Rangemaster cooker which has a rating of 14kw.

This cooker has a couple of ovens and grills and induction hobs - it's a beast

My question is regarding the cable / isolation switch rating, I know there is some debate over the issue but I reckon being realistic there is no chance that the cooker will ever run at full capacity and that a 6mm cable covered by a 40a MCB (only 5m run from board no insulation under floor) and a 45a DB switch would suffice.

The other option would be a 63a MCB with 10mm cable and a 63a rotary isolator.

The house is occupied by a couple and soon to be baby.

What would you guys do in this situation?
 
Yep, as others have said, 6mm on a 32A will suffice, change it for a 40A if you want some double assurance.

I had this argument with AGA on behalf of a customer just before Christmas - they were buying a (rebadged Rangemaster) AGA range and the Aga installers were stipulating that it HAD to be installed on a 10mm cable and a 50A CPD. Story short, I battered the head of Aga Technical into submission down the phone until he'd done the maths himself....and the result, after using every individual item at the exact rating, was something like 25A (can't remember exactly). So AGA ended up looking like a right spanner, I saved the customer probably £500 for not having to install a new circuit and I got to charge for a couple of hours of my time, spent solely on the phone.
 
To play the devils advocate, what was the rating of the cooker? Taking 6mm as good for 47A (11kW) and a 32A C/B good for 45A on slow overload, you're pushing the extreme of the cable and the end tolerance of the C/B?. Good design practise?

Changing for a 40A C/B could give you upto 60A on slow overload -- more than the cable can take?
 
I know that diversity is applied for a cooker circuit, but what happens at Christmas for example, when she is running full tilt?

The same thing as will happen on any other day when it's on at full chat!
The current drawn will be that calculated according to diversity (apart from possible small/short term overloads)
 
The same thing as will happen on any other day when it's on at full chat!
The current drawn will be that calculated according to diversity (apart from possible small/short term overloads)

Not to sure I agree there! Diversity takes into account the likelyhood you wont be at full power ...... if you are cooking Sunday lunch for the street you may well have everything on at 100%!
 
Diversity takes in to account the operating characteristics of cookers.
Temperature is controlled by switching elements on and off via a thermostatic control of some type. This leads to only a certain quantity of the total power being connected at any one time.
Over many years the diversity calculations have been adjusted and improved to reflect this accurately.
 
i dont know what it is with some in here...

but theres this continuing lack of understanding goin round about diversity....

as has been quite rightly said before its unlikely that all loads will be on at once...and even if a large portion of them were...once upto set/operating temprature the stats kick in...and just keep everything ticking over nicely.

now, taking into consideration that an MCB with characteristics to BSEN60898 will hold for upto 1.45 X its operating current for upto an hour before letting go...and the fact that the stats will be constantly making & breaking...then its unlikely that current draw will get anyware above 40A..is it

and in fact i dare say that a 32B would suffice...

there..i`v said it now...
 
The key to that is whether the max demand given by the manuf is the max demand for each individual element added up or the maximum demand when everything is fully loaded and diversity is applied (i.e. the fact that the loads will be cycling on/off and not all on at once at full tilt!)
 
I wonder if it's has its roots in the throwaway society? Apprentices don't get to do cooker repairs and so don't learn how a cooker works anymore?
It's just another magic box, just like the tellybox / microwave / fridge, I don't know the details but know the basic principal of their operation.

The same seems to be true with cars these days, so many people will happily drive them around but haven't got a clue about how they work.
 
The ratings will normally state maximum connected load, ie. all the elements and any controls added together.

I've seen both, where you can actually tot up the individual loads and come to the max load the manuf states, and others where the manuf states the max load includes diversity and it doesnt add up to the individual loads!
 
Only in the textbooks, in the real world we still have 240V.
And really it should be at the voltage stated on the ratings plate. These days you tend to find the rating at 240 and the rating at 230 on a lot of rating plates.

of course I understand it's 240 in reality and why it's 230 to save manufacturers money, but I'm pretty sure calculations are made with nominal figure
 
It's not 230 to save money! It's 230 because our European masters decided we should lower our voltage to harmonise with the rest of Europe (who ignored it, just like the colours change)

If an appliance is rated at 10KW at 240V you use 240 in your calculation, if it's rated at 230V then you use 230. You'll only introduce an error in to your calculation otherwise.
 

Reply to Beast of a cooker in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
655
  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
668

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top