Bedroom lights without earths
Here is another question. In my bedrooms 1 light is earthed and two are not. The lights are pendants..All plastic fittings. I have been told there needs to be further investigation. The investigation apparently needing to get up in to the loft to look for the earth. This is a problem for me as the loft is looked and choker block with my stuff. Loads of it. The loft is locked and I am not sure where the key is. (Lockdown intervened(.Anyhow I have asked the electricians why they need to investigate further. I said I thought it was okay that bedroom lights are not earthed with plastic fittings. They just dont answer. I am feeling a bit desparate about it as I have 28 days to complete the work
For what it’s worth, my thought is :
- the report from 2014 was in error to conclude no CPC present at the light was ok. So the C2 of the recent report doesn’t indicate a change in regulations, in my view. If there was an earth present at the lighting point but it had been cut somewhere, that would be seen as potentially dangerous and require fixing. So I see the “no earth at light” in the same way.
- the loose trunking, well I haven’t seen it so I can’t judge whether it’s potentially dangerous, but it’s certainly poor workmanship and would now require some metal clips to prevent premature collapse in the event of a fire. If it’s in a trafficable location where it may be grabbed and pulled then I would think that’s potentially dangerous. In any case it should be fixed as they can further deteriorate and become unsafe between inspections.
The earth return path is a vital part of how the circuit breakers (MCB‘s) or fuses in the consumer unit (CU) work to disconnect the supply in the event of a fault. This is known as protection by automatic disconnection of supply, or ADS. The CPC (earth) provides a low resistance path back to the CU for any potential fault current, hopefully preventing that harmful current from flowing through a person in the worst case scenario. That’s why a CPC should be present at all points of the fixed wiring and should ideally run alongside the live conductors of each circuit.
ADS is like the bare minimum requirement for protection from electric shock and RCD’s provide an additional layer of protection on top of that.
Some faults don’t create enough current to allow the MCB’s or fuses to operate, or they allow more current than is typically survivable to flow through a person before they do disconnect the supply. Residual Current Devices (RCD’s) provide additional protection against these by being more sensitive to smaller current imbalances in the circuits they protect. They monitor the outgoing and return current on the line and neutral conductors of a circuit or group of circuits and trip if the imbalance is more than 30mA (other ratings are available, but 30mA is required for additional protection). They don’t need a CPC to operate but having one provides that low resistance path back to the CU for the fault current, causing the RCD to see the imbalance in the live conductors (L + N) quickly and trip accordingly.
Electricity is sort of like water in that it usually follows the path of least resistance. In the event of a fault with a CPC present, the electricity will flow down that and should trip either the RCD or MCB/fuse before anyone gets hurt. Without a CPC it’ll flow through the next path of least resistance which might well be the unfortunate human being who’s just stuck a nail through a cable above a light switch.
Hypothetically (really don’t try this at home), grabbing the end of a single line conductor (usually brown or red in the UK) won’t cause an MCB or fuse to trip or rupture before you’ve had a very nasty, possibly fatal, shock. They might not even operate at all in some circumstances. If we fit a 30mA RCD as well it will trip quickly enough to prevent that same shock being fatal in most cases.
Thank you for this. Is it that the regs since 2014 have made the earth mandatory. As the EICR done then was passed. Intact since then there is more things earthed in the house
No, the regulation applied to all circuits from the early 1970’s I think. Prior to that lighting circuits could be wired in 2-core cable without a CPC.
As @Wilko says it sounds like the 2014 report was incorrect, but again it’s very difficult to comment on either report with certainty without seeing them or the property in question. It sounds like the concern of the recent inspector is that a CPC is present at some fittings but not all of them. I’d certainly see that as a potentially dangerous situation and would want to investigate it.
Perhaps I am wrong about the 2014 saying there was no earth. I have this EICR and can post it online. Well hopefully as I am crap at putting things online. Prob is I need to doctor it as well to get rid of who did it as well the address. I am getting more and more confused not less. Actually I don't think there was an earth in 2014. Pretty certain there wasnt
Hi - not meaning to teach you how to suck eggs or to say you have to post a doc, but I put a post-it-note across stuff and take a pic. Very low tech :) .
Only will be how to attach said photos on here. I guess there must be some place to do this. Ahh may be it's that symbol
I guess it's that symbol up the top to attach it.
Any guidance I've seen (from schemes and the best practice guide from electrical safety first) have no RCD on domestic lighting circuits as C3, they also have no cpc on lighting circuit with class 2 fittings and plastic switches as C3 (if they are wired in a 2 core cable without an earth- this might not be the case here as 1 light has a cpc, hence the FI code).
I know neither is ideal and a strong recommendation for improvement would be given (I'm sure most people would happily pay to improve safety in both of these situations), but a lot of you seem to give C2 for both of these making the report unsatisfactory and therefore forcing the improvements.
If it were not for the problem with accessing the loft I would not be hesitating. What difference does it make that one light has a CPC? This what I have wondered about? Would it be better if there were none?
It would not be better no. Removing a CPC is never an improvement!
Removing one no, but if it never had one in the first place because it was wired in twin that doesn't have a cpc, then the class 2 fittings and C3 would apply- doesn't seem to be the case with yours though as one fitting has a cpc so likely to be wired in t&e
The problem is we don’t know what “no earth” actually means without seeing the report or the property.
It could be that a CPC is only physically present at one fitting, which is confusing and requires investigation to find out why. Older properties may only have 2-core to all the light fittings and switches and that is sometimes ok but with a strong recommendation to upgrade.
Or it could be that a CPC is physically present at all light fittings, but not continuous between them. This is much more serious as it implies a break or degradation in the wiring somewhere, possibly rodent damage or a poorly made joint somewhere.That needs further investigation and must be resolved.
Or the wiring could leave the DB in 2-core, turn into 3-core at one fitting and then back to 2-core at the others. Which again implies a joint somewhere, and maybe not a great one at that. Further investigation needed.
Thanks for this. I am understanding it better now. I don't think there has been
What you also need to realise is coding is done at the discretion of the inspector so just because the majority on here may say C3 for no cpc with plastic class2 fitting......another inspector who to be fair is actually on site and can see/test the installation may decide it’s a c2 and that’s what your report will reflect.....possibly maybe if you ever see it ?