Posted this on the Napit forum but had no respite se despite lots of views so thought I would paste it on here.
Interested in your opinions
afternoon all,
after some opinions on a job I have been asked to price. Spoke with another NAPIT member and to be honest not sure if we are being over cautious.
The current set up is an absolute abortion and the new manager has come in and wants it sorted out section by section.
Have been asked to fit a sub board on a waste management site to provide power at the other end of site for some cabins and a couple of commando sockets. The existing supply is pme intake cupboarding with a 6 way TP&N DB supplying lighting, cabins and some plant. All cables run (left laying) surface in SWA. No RCD except on the sub boards inside the cabins.
I am planning on running a new supply from this DB through a duct in the road to other side of some gates and then clip along the fence (they may fit a split duct after) along to a new DB. From here, supply the new cabins and commando sockets in SWA. The commando sockets would have rcd protection at the socket end, the cabins would have it in their own DB.
Question is, should there be rcd protection on the cables feeding the new cabins and sockets? The cable will be visible, SWA, marker tape used but due to the nature of the enviroment should it be classed as a construction site? Thinking about putting a time delayed 300ma as main switch on new DB but then am I being over cautious? Its not a building site but there is a lot of plant movement. If I fit this, why not fit it at the original DB and protect that cable too? Then while Im at it do the existing cables need protecting too?
See what I mean
What the other Napit guy (and myself) believe is to go with the 300ma main switch on the new DB to cover my rear (as the site is deadly enough as it is, will post some pictures when I get time) but obviously this will be pushing the price up.
Dont even start me on the extending PME I have just thought of................
Sent from my iPad using Tapatalk HD
Posted this on the Napit forum but had no respite se despite lots of views so thought I would paste it on here.
Interested in your opinions
afternoon all,
after some opinions on a job I have been asked to price. Spoke with another NAPIT member and to be honest not sure if we are being over cautious.
The current set up is an absolute abortion and the new manager has come in and wants it sorted out section by section.
Have been asked to fit a sub board on a waste management site to provide power at the other end of site for some cabins and a couple of commando sockets. The existing supply is pme intake cupboarding with a 6 way TP&N DB supplying lighting, cabins and some plant. All cables run (left laying) surface in SWA. No RCD except on the sub boards inside the cabins.
I am planning on running a new supply from this DB through a duct in the road to other side of some gates and then clip along the fence (they may fit a split duct after) along to a new DB. From here, supply the new cabins and commando sockets in SWA. The commando sockets would have rcd protection at the socket end, the cabins would have it in their own DB.
Question is, should there be rcd protection on the cables feeding the new cabins and sockets? The cable will be visible, SWA, marker tape used but due to the nature of the enviroment should it be classed as a construction site? Thinking about putting a time delayed 300ma as main switch on new DB but then am I being over cautious? Its not a building site but there is a lot of plant movement. If I fit this, why not fit it at the original DB and protect that cable too? Then while Im at it do the existing cables need protecting too?
See what I mean
What the other Napit guy (and myself) believe is to go with the 300ma main switch on the new DB to cover my rear (as the site is deadly enough as it is, will post some pictures when I get time) but obviously this will be pushing the price up.
Dont even start me on the extending PME I have just thought of................