Hey up, trying to think of the best way to do a job, the incomming supply is TT and is located at the bottom of this fellas drive in a brick bunker, need to get a supply to the house ( 39m away ) and to his garage (16m away from the bunker).

Firstly can I use a 100ma rcd instead of a switch fuse at the supply end or do I have to install both?

Looks like I'll have to run 35mm 2 core SWA to the house, am i ok using the armour to export my earth or should i be using 3 core? and I take it it's ok to use the rod in the bunker as my earth for the whole site ?

Might be daft questions but my heads gone now thinking of all the different ways i could do this job.

Any advice would be great, Cheers.
 
Sorted this, just needed to sleep on it.

100ma Rcd, into switch fuse, on to house. Easiest way I reckon. Overload and earth fault protection.

Can I use the armour of my 35mm 2 core ?, can't see why not.

My rod in the bunker will be sufficent for the whole site, again no reason why it shouldn't.

Confused myself with too much thinking.
 
Since i assume there will be main bonding to be carried out in the house you will need to check that the CSA of the armouring will be suitable to be used as both the CPC of the submain circuit and as a main bonding conductor.
 
I havent looked it up but 62 sounds a little on the large side. 62 sounds more like the actual steel CSA the copper equivilant is probably half that. Just have to double check to be sure.
 
use the swa as the cpc for the sub main and isolate it from the house,then plant a new rod at the house and take a new earthing conductor to the met in your consumer unit which creates a new tt supply soley for the house. and when your trying to achieve discrimination between the two rccbs refer to table 41.1 for your max disconnect times.0.2
 
Steve thats how I was going to do it, till I started thinking do I really need to stick another earth rod in.

I havent looked it up but 62 sounds a little on the large side. 62 sounds more like the actual steel CSA the copper equivilant is probably half that. Just have to double check to be sure.

Right I take it I can use either the adiabatic equation or the table 54.7 method to work this out, is this correct ?

I thought I compared my result with the actual steel csa, am i barking up the wrong tree here or what?

When you say look it up, where do you find this information?
 
The adiabatic equation can be used to size the cpc, and main earthing conductor, but not the main protective conductors these have to-be sized from table 54.8 and copper is used,or another material affording equivalent conductance.

to work out the copper equivalent of a steel wire armour you first have to find the manufactures data for the cable
find the
ohms/km for the copper conductor divided by the ohms/km for the armour.
multiply the answer by the copper conductor size and that will give you the copper equivalent of the swa
then multiply the copper equivilant by 8.8 and that will give you the swa c.s.a
 

Reply to Best Method For TT Dis Cct in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
591
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
1K
Personally I always use Denso tape. Although watch your hands when applying it - it's pretty messy stuff.
Replies
7
Views
366

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top