ive been asked to rewire 5 flats , each flat is on a card meter, a new cu is to be installed in each flat to cover 3/4 circuits,
a new landlords main board is to be installed by the front door, can each flat be isolated from the main board or does each flat need individual isolation like it is now . What size run of cable to each flat 6mm or 10mm, only one flat has a electric shower , two flats have an electric oven. The flat with electric shower doesn't have electric oven.
[ElectriciansForums.net] best way for isolation
 
Last edited by a moderator:
All of the flats could be fed from a single DB, however it should not be an MCB distribution board. For any hope of discrimination each flat needs to be fed via a fuse or possibly an MCCB.
With that in mind it will almost certainly be cheaper to install a switched fuse for each flat supply.
Then there is also the future convenience of operation to be considered, it will be far better to have seperate switchgear for each flat to allow any future work to be done without disturbing other flats.

The size of the supply for each flat needs to be calculated and the cable size calculated.
If you have been a trainee but aren't now then that implies you are now, and fairly recently, fully qualified so you should have the knowledge to carry out cable calculations far better than just guessing at 6/10 maybe.
 

Reply to best way for isolation in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
494
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
973
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

Depending on the location of the 2 CU's and the quality of materials I'd say £10K-12K. If they're potential tyre kickers don't waste loads of time...
    • Informative
Replies
4
Views
339
I would hazard a guess your electrician may be able to contact your DNO and have the switch swapped to a MFS very quickly..
Replies
13
Views
775

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top