Hi guys
I am taking on a job of supplying/wiring a summer house which is in the process of being built.
Consumer unit has no spare ways so my only option really is splitting the tails in the meter cupboard into a fused isolator to supply the SWA. However as far as I’m aware I am not allowed to install an isolator in the meter cupboard and the client is getting this signed off by the council so I need to do everything properly. Are there any ways around this? Even if I wanted to add a new CU I would still have to split the tails so it seems to me that there is no way around this.
Also the summer house is only going to have 10x sockets and 6x spot lights so I don’t see any reason to use anything bigger than 6mm SWA. Main cutout is 100A so I will need a fused isolator to step the amps down to 32A (SWA is running in duct under the floor) do they even make an isolator like this? 63A is the lowest I’ve seen so I will have to run in 16mm SWA to support the 63A from the isolator? Seems overkill to me
I am taking on a job of supplying/wiring a summer house which is in the process of being built.
Consumer unit has no spare ways so my only option really is splitting the tails in the meter cupboard into a fused isolator to supply the SWA. However as far as I’m aware I am not allowed to install an isolator in the meter cupboard and the client is getting this signed off by the council so I need to do everything properly. Are there any ways around this? Even if I wanted to add a new CU I would still have to split the tails so it seems to me that there is no way around this.
Also the summer house is only going to have 10x sockets and 6x spot lights so I don’t see any reason to use anything bigger than 6mm SWA. Main cutout is 100A so I will need a fused isolator to step the amps down to 32A (SWA is running in duct under the floor) do they even make an isolator like this? 63A is the lowest I’ve seen so I will have to run in 16mm SWA to support the 63A from the isolator? Seems overkill to me