Hi,

I'm looking for some guidance from more experienced hands. Have a friend who just bought a 2.2kw air compressor which is obviously blowing the fuse in the plug due to the start-up current. Manufacturers information suggests a 30a single phase motor DOL for the power rating whilst the person who sold it said it needs a 15a fused spur.

The compressor won't be installed on its own circuit with a type c circuit breaker so wondering what the best route to take given a fused spur off the ring is limited to 13a also? Someone suggested an unfused spur to a 16a single phase 2P+E connector and plug like you see at caravan parks which could cope with the start up current but any guidance much appreciated.
 
A little confused here, you say the manufacturer suggest fitting a DOL starter, doesn't this compressor already contain its own integral control?... or am I getting it wrong, a 2.2 kw single phase would have the effective inrush of a 5.5 to 7.5 kw 3ph so yes a 30amp front end type c would be recommended although you could use a permanent 16amp connection.
 
I agree but he sort manufacturers guidance which usually refines the worst case scenario those charts are based on. The higher the mcb the more problematic complying with ELI which makes advice difficult without having more info.
 
My own experience is mostly small motors (<= 1kW) under electronic servo control, there the protection is more about stopping fires if/when the electronics fail.
 
Try a 13A time delay (slow blow) fuse in the plug ? ?

I know this was said tongue-in-cheek but for those not familiar with fuse specs, normal 'slow-blow' cartridge fuses will not have the breaking capacity (nor will they correctly fit a 13A plug) and must not be used for this application.
 

Reply to Best way to connect up air compressor in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
How did it go?
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top