I’m 75 and am not an electrician although I’m pretty handy and attended a CnG Domestic Wiring course 30 years ago. If friends or relatives have electrical problems I have always been able to source the problems and rectify them.
HOWEVER, I AM OUT OF MY DEPTH with this problem.

Garage about 5m from bungalow, power directly fed by 4mm, 3 core SWA from a 32A trip. Mini DB in garage serves lights (6A) and a few sockets (32A).

The 32A feed in the bungalow is continually tripping and also trips the main RCD.

I disconnected the garage DB completely so no connections at all in there, but the 32A feed trip in the main DB still blows.

The installation in the main DB looks sound and there shouldn’t be any rodent problem as it has SWA.

It appears to be worse in colder weather.

Any ideas please ?
 
The cable needs tested between house and DB.

you disconnected the garage db from the cable, but not the cable from the house db? is that right?

Moisture can still get into SWA, and maybe its damaged through spade work, or even just stones settling in the ground. The trench was buried in should be bedded with sand.

Remember, RCD's will trip with a fault between neutral and earth as well as live and earth..... if the 32A mcb is switched off, the neutral of the cable is still connected and can trip the rcd.
 
I’m 75 and am not an electrician although I’m pretty handy and attended a CnG Domestic Wiring course 30 years ago. If friends or relatives have electrical problems I have always been able to source the problems and rectify them.
HOWEVER, I AM OUT OF MY DEPTH with this problem.

Garage about 5m from bungalow, power directly fed by 4mm, 3 core SWA from a 32A trip. Mini DB in garage serves lights (6A) and a few sockets (32A).

The 32A feed in the bungalow is continually tripping and also trips the main RCD.

I disconnected the garage DB completely so no connections at all in there, but the 32A feed trip in the main DB still blows.

The installation in the main DB looks sound and there shouldn’t be any rodent problem as it has SWA.

It appears to be worse in colder weather.

Any ideas please ?
You need some test equipment to be able to do an Insulation resistance test on the cable that feeds the garage.
 
looks like you may have a damaged cable.
can you measure the resistance between the 3 cores?
 
The cable needs tested between house and DB.

you disconnected the garage db from the cable, but not the cable from the house db? is that right?

Moisture can still get into SWA, and maybe its damaged through spade work, or even just stones settling in the ground. The trench was buried in should be bedded with sand.

Remember, RCD's will trip with a fault between neutral and earth as well as live and earth..... if the 32A mcb is switched off, the neutral of the cable is still connected and can trip the rcd.

Thanks for that.
Yes, that’s right.
I hear what you’re saying, I suppose I considered the cable bullet proof as it hasn’t been touched in 10 years that we know of, and there’s been no problems with it.
 
SWA can get damaged during / after installation or may have already been damaged before installation where the outer sheath gets cut.
This isn't a problem to start with but as the steel armour corrodes within the outer it can put pressure on the inner cores and break through the insulation.
All you need then is some moisture and you have a fault.
 

Reply to Beyond me ! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
462
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
952
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
897

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top