I am currently in the process of bidding for a job. Its an old building that the owner wants to convert into 15 one bedroom self-contained flats. Each room will have a 8.5kw shower, 3kw panel heater, 3kw water heater and a 5kw cooker, plus a few sockets and lights etc. Each flat will have its own C.U inside the flat. But I'm looking for a bit of advice on whether I should use 16mm or 25mm metre tails, and if I should use a 60a or 80a sp&n fuse switch, to power each individual flat from each individual meter.
The furthest length a pair of tails will have to travel is 25m.
Bearing in mind that these are one bedroom flats, and it is highly unlikely someone is stupid enough to have the hob on whilst taking a shower. Will 16mm do?
 
I've done that on some apartments, bemco unit to meters, you'll have to put all the 100mm trunking in place for that with the earth cables in place to your 80a switched units, we then run 16mm 3 core swa to each apartment, terminated by gland to a box with a Henley block in, 16mm tails to your consumer unit,
 
yea defo use swa instead of meter tails, that way its protected and earthed, 16mm swa is pretty stiff stuff so not very good to gland straight to flimsy plastic consumer unit, and the glands are quite wide so not a lot of meat left around it if you did?
 

Reply to Bidding for job in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top