I'm currently doing the 2357 City and Guilds coursework at this precise moment, but i cannot seem to get my head round what should be a simple process in the design area.
Hopefully you guys will be willing to help me get round this first question so i can understand and complete the remaining questions.
Its regarding the minimum size CPC for 'each circuits' (one only provided).
I need to give consideration to disconnection times and thermal constraints.
Here is the details i have so far.

Prospective fault current - 50 kA -(doesn't seem right)?
400v Supply three phase
Ze of 0.008
i need to work out the CPC size for a 5kW 400v 3 phase machine.

I've looked in the Wiring regs and even looked at the adiabatic equation but still cannot get my head around it.
I know the following:

S is the nominal CSA of the conductor in mm[SUP]2[/SUP]
I is the value in amperes of fault current
t is the operating time of the disconnecting time in seconds. (But would that be type C circuit breaker? and what sort of time would i need to give for the above circuit?? 0.1 or 5?)
k being the factor of resistivity and temperature of the material.


A walk through talk through would be appreciated?

Thanks in advance.
 
What type of protective device had been given?

I had to choose the protective device.

These are the calculations i had made a while back relating to this machine
i). 5kW, 400V three-phase machine
*Design current = 12.5A
*Overcurrent device = 16A
*Wiring enclosed in Metallic trunking
*Ambient temperature of 25degrees C
*Tabulated current = 23.98A
*Size Cable required = 4mm[SUP]2[/SUP]
*Length of cable required –19.4m
*Voltage drop = 2.3V
 
I had to choose the protective device.

These are the calculations i had made a while back relating to this machine
i). 5kW, 400V three-phase machine
*Design current = 12.5A
*Overcurrent device = 16A
*Wiring enclosed in Metallic trunking
*Ambient temperature of 25degrees C
*Tabulated current = 23.98A
*Size Cable required = 4mm[SUP]2[/SUP]
*Length of cable required –19.4m
*Voltage drop = 2.3V

You might want to re-check your previous calculations, the bits highlighted in red first.
 
Depends on how you calculate it,

kW / (Line Voltage X root 3)

or (kW / line voltage) / root 3

When you are given the kW value initially, it simplifies the calculation somewhat,as the PF and EF is already taken care of in the final kW value.

It is not as simple working the calculation forward. for where a motor/machine is involved then: Power (Watts) = 1.73 Ă— Line Volts Ă— Line Amps Ă— PF Ă— Efficiency.


Calculate it again, you are nearer.
 

Reply to Bit confused in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

Similar threads

https://sravivarman.com/technical-articles/parallel-operation-of-thyristors/ Series resistor, or bigger series resistor, needed?
Replies
1
Views
151
  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top