The Ghost
This is fed in 2 core 4/6mm (not positive) SWA. No earth except a bit of 2.5mm (blue sheathed with earth) on pirhana nut to earth bus bar. An atrocious install technique all round. The landlord did it. Swearing heartily at the spark who did not finish the job. Wrong MCB for the 2.5 on two of them. All radials serving a kitchen (commercial) Was called to inspect (not EICR) to give an opinion on the state of the installation. No certificates by the Landlord or Electrician who put the supply in (of course) This type of wiring evident throughout by the way not just the kitchen I was looking in. I mean a Landlord who cannot and should not install electrics commisioning ccts with no tests. How may laws is he breaking. Where do I begin with the clients? I am speechless at the moment. Ideas? I just can't decide wtf to say to them. Did Zs and RCD tests all met regs, tested all the points. You can see 32a mcb on 2.5 and 6a on 2.5 supplying four double sockets feeding 2 x 2kw induction hobs, bain marie and so on. I'll stop there for now.